Fuse ratings and ovens - replacing double with two singles
Options

Doc_N
Posts: 8,543 Forumite


I have a double oven in place at the moment (7.2 Kw per the rating plate).
Planning to replace it with two single ovens, each rated 3.6 Kw.
There's a 32 amp fuse, and logic suggests that there won't be any problems replacing the double oven with two singles.
Am I right?
Planning to replace it with two single ovens, each rated 3.6 Kw.
There's a 32 amp fuse, and logic suggests that there won't be any problems replacing the double oven with two singles.
Am I right?
0
Comments
-
yes its fine0
-
The fuse is for the cable not the appliance so it'll be fine. Just make sure that any cable going to each oven is appropriate as well.0
-
Thanks guys.0