Radiator Feed Before Zone Valve ?
Never associate with idiots on their own level, because, being an intelligent man, you'll try to deal with them on their level - and on their level they'll beat you every time.
Being hated by idiots is the price you pay for not being one of them.
Jean Cocteau 1889-1963
Comments
-
Many modern boilers require pump overrun I.e. the pump to continue to circulate water after demand ceases for a few minutes to cool the boiler heat exchanger. For this to work there needs to be a path to circulate. Perhaps that radiator is part of that path?
Not a fan of that method for the reason you located -heat output when not required. Better solution is to have 3port diverter valves connected such that there is a secondary circuit for circulation when neither heat or hot water is demanded. This can be through the radiator circuit through an uncontrolled radiator that is always 'open', typically bathroom as the very small bit of extra heat is not really an issue for the short overrun time (5 minutes typically) but you are ensured that boiler overrun works well.
Might not be like that on your system though
0 -
I agree with Ainsley1. It's a bypass.0
-
Been on line looking at installation instructions for the boiler and it seems the only feasible / simplest way to stop this rad heating up needlessly is to convert to a Y plan system as it states a bypass is not needed as it automatically diverts to HW when there is no demand. It may lead to a longer over run though as it is a simple 80 deg switch dissipating into hot water rather than cool air but will be on a longer piped run using 22mm. Now need to check if there is 3 core going to the tank stat. (although it may be fairly easy to run as the tank is almost directly above the wiring centre on stud walling)
Never associate with idiots on their own level, because, being an intelligent man, you'll try to deal with them on their level - and on their level they'll beat you every time.
Being hated by idiots is the price you pay for not being one of them.
Jean Cocteau 1889-1963
0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 355.4K Banking & Borrowing
- 254.7K Reduce Debt & Boost Income
- 456K Spending & Discounts
- 248K Work, Benefits & Business
- 605.3K Mortgages, Homes & Bills
- 178.9K Life & Family
- 263.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards