Radiator Feed Before Zone Valve ?

molerat
molerat Posts: 36,322 Forumite
Part of the Furniture 10,000 Posts Name Dropper Photogenic
My son has just moved into a house. We put the boiler on to get hot water and noticed the uncontrolled rad in the hallway getting hot. I thought maybe the zone valve was stuck but no other rads were on so went and had a play and noticed a tee between the pump and zone valve with microbore running off, I assume, to the radiator on the other side of the wall. The previous owner said she hardly needed the heating on - not surprising as the hallway rad is on all the time HW is selected. The question is - is this normal and if so why ? Open vented system all on microbore BTW.

Never associate with idiots on their own level, because, being an intelligent man, you'll try to deal with them on their level - and on their level they'll beat you every time.

Being hated by idiots is the price you pay for not being one of them.

Jean Cocteau 1889-1963

Comments

  • Ainsley1
    Ainsley1 Posts: 404 Forumite
    Many modern boilers require pump overrun I.e. the pump to continue to circulate water after demand ceases for a few minutes to cool the boiler heat exchanger. For this to work there needs to be a path to circulate. Perhaps that radiator is part of that path?
    Not a fan of that method for the reason you located -heat output when not required. Better solution is to have 3port diverter valves connected such that there is a secondary circuit for circulation when neither heat or hot water is demanded. This can be through the radiator circuit through an uncontrolled radiator that is always 'open', typically bathroom as the very small bit of extra heat is not really an issue for the short overrun time (5 minutes typically) but you are ensured that boiler overrun works well.

    Might not be like that on your system though :)
  • Crinkmeister
    Crinkmeister Posts: 473 Forumite
    I agree with Ainsley1. It's a bypass.
  • molerat
    molerat Posts: 36,322 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 31 May 2016 at 12:15AM
    Been on line looking at installation instructions for the boiler and it seems the only feasible / simplest way to stop this rad heating up needlessly is to convert to a Y plan system as it states a bypass is not needed as it automatically diverts to HW when there is no demand. It may lead to a longer over run though as it is a simple 80 deg switch dissipating into hot water rather than cool air but will be on a longer piped run using 22mm. Now need to check if there is 3 core going to the tank stat. (although it may be fairly easy to run as the tank is almost directly above the wiring centre on stud walling)

    Never associate with idiots on their own level, because, being an intelligent man, you'll try to deal with them on their level - and on their level they'll beat you every time.

    Being hated by idiots is the price you pay for not being one of them.

    Jean Cocteau 1889-1963

This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.4K Banking & Borrowing
  • 254.7K Reduce Debt & Boost Income
  • 456K Spending & Discounts
  • 248K Work, Benefits & Business
  • 605.3K Mortgages, Homes & Bills
  • 178.9K Life & Family
  • 263.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.