(just 4.1% which is below the allowable 5%)
The 5% for power and 3% lighting is not actually a Regulation, but is stated in an Informative Appendix to BS7671. Proper functioning must be ensured by Regulation.
That said, 4.1% on an extension lead completely ignores the voltage drop on distribution circuits and final circuits, which may already have seen a couple of percent or more.(yes, it will just fit in a "normal" BS1363 13A plug, but I'd use proper commando connectors & make up a small patch cable to a "normal" plug.)
Regardless of whether it fits the plug or not (which generally it won't) it is not permitted to wire a BS1363 plug with 2.5mm^2 flex. It directly contravenes BS1363.0 -
Regardless of whether it fits the plug or not (which generally it won't) it is not permitted to wire a BS1363 plug with 2.5mm^2 flex. It directly contravenes BS1363.
[So long as the 2.5mm cable will fit and can be clamped in the cable grip there is no danger and (unlike the 16A Commando Plug) contains an integral cartridge fuse for additional safety.]
Scrounger0 -
Sometimes the law is an A$$$ :rotfl:
[So long as the 2.5mm cable will fit and can be clamped in the cable grip there is no danger and (unlike the 16A Commando Plug) contains an integral cartridge fuse for additional safety.]
Scrounger
2.5mm^2 does not properly fit a BS1363 plug and must not be used with one.
Also, a cartridge fuse does not provide additional safety where a 2.5mm^2 flex is used as this is already protected by the 16A / 20A protective device. The purpose of the fuse is simply to protect the cable and not for any other purpose.0 -
2.5mm^2 does not properly fit a BS1363 plug ...
Perhaps we have discovered a requirement a special 'high-spec' 13A plug designed for thicker cables (for long runs, thicker jackets, armoured mains cables etc) ?Also, a cartridge fuse does not provide additional safety where a 2.5mm^2 flex is used as this is already protected by the 16A / 20A protective device.
For all we know the supply in this case could be straight from a CU 32A breaker (or fuse wire).
Even if it is fed from a CU breaker, IMO it is much better to have an additional local 13A (or less) fuse in the circuit (in addition to the CU breaker or fuse which could be much larger capacity). Belt and braces.The purpose of the fuse is simply to protect the cable and not for any other purpose.
Scrounger0 -
-
Perhaps we have discovered a requirement a special 'high-spec' 13A plug designed for thicker cables (for long runs, thicker jackets, armoured mains cables etc) ?
There is no requirement as none of these things are appropriate for a BS 1363 plug. There are other - better and correct - options which can be used if any of these things are necessary.
A 2.5mm^2 cable connected to a BS 1363 plug is NEVER compliant with the Standard.0 -
The instantaneous starting current of the motor may be a lot more than the nominal 3 kW rating of the motor, which will affect the voltage drop calculations.
I agree with Zax47; the practical approach is to make up a 2.5mm 25 metre extension lead using 16 A 'Commando' connectors with adapter leads at each end - although if it's for this application only I'd change the plug on the appliance to 16 A, and fit a 16 A 'coupler' flying socket on the extension lead, so only need a 13 A - 16 A adapter lead at the supply end.A kind word lasts a minute, a skelped erse is sair for a day.0 -
Hi, well I got hold of a multimeterand checked the voltage. At the house it is 243v (although it was 236v sunday after dark when i guess lots of people were using electricity) and also 243v in the barn. This was a no load reading- do I need to have a powerful appliance running to get a true idea of how the voltage drops?0
-
Hi, well I got hold of a multimeterand checked the voltage. At the house it is 243v (although it was 236v sunday after dark when i guess lots of people were using electricity) and also 243v in the barn. This was a no load reading- do I need to have a powerful appliance running to get a true idea of how the voltage drops?
You are over thinking this.
Just buy a reel of 1.5mm T&E and get splitting them logs!
The induction motor will run fine down to 220V and probably much lower with no problems. It will likely have thermal overload built in for self protection.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.6K Banking & Borrowing
- 252.9K Reduce Debt & Boost Income
- 453.3K Spending & Discounts
- 243.5K Work, Benefits & Business
- 598.3K Mortgages, Homes & Bills
- 176.7K Life & Family
- 256.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards