Building regs for sockets near sink

I've hit a problem planning the sockets in my kitchen extension.

I've put the sink on the far right (see picture) and assumed I could have some sockets (in red) on the wall as far from the sink as possible (400mm away).

My electrician has just told me that to pass building regs they need to be 800mm away from the sink. After a quick Google search, I can only find threads saying 300mm is necessary. Can any electricians confirm it's 800mm?

kitchen.png

Comments

  • Biggles
    Biggles Posts: 8,209 Forumite
    1,000 Posts Combo Breaker
    Larda? DW?
  • Sanoffo
    Sanoffo Posts: 57 Forumite
    Eighth Anniversary Combo Breaker
    DW - Dishwasher
    Larda - Larder cupboard
  • zax47
    zax47 Posts: 1,263 Forumite
    300mm, even then it's in BS7671 ("17th Edition Wiring Regs") which is only "guidance for best practice". It's as close as I fit them. :-)

    Not sure where he gets 800mm from, thats nearly a metre! Should be RCD protected anyway so no biggy. Worse is when I find then BEHIND a flippin hob!
  • System
    System Posts: 178,303 Community Admin
    10,000 Posts Photogenic Name Dropper
    I must admit that the only references I can find are the minimum 300m.

    I would ask your electrician to show you evidence of the 800mm requirement. It should be in the 17th edition of IEE wiring regulations which isn't free to download so can't check
    This is a system account and does not represent a real person. To contact the Forum Team email forumteam@moneysavingexpert.com
  • heretohelp
    heretohelp Posts: 133 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    I may be wrong but I don't think there is a distance mentioned in the 17th edition a proper sparky will be along to tell you if I am right or wrong.
    I think the building regs mention 300mm as a minimum so 400mm would be ok.
  • Sanoffo
    Sanoffo Posts: 57 Forumite
    Eighth Anniversary Combo Breaker
    Great thanks, I thought 800mm was quite far. I've seen some tiny kitchens so wondered how they would get any sockets in there.

    So I won't have a problem failing building regs?
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243K Work, Benefits & Business
  • 619.9K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.