Electric shower wiring question

I currently have a Triton T80i electric shower which is an 8.5KWh model. It was fitted about 10years ago. I wanted to know whether I could change it for a bigger KWh rated model and if so what is the max I coulod go to?

Is there any way I could check this myself without calling out the experts? I currently have a 40A fuse fitted in my consumer unit which controls that circuit.

I don't really want to go down the route of changing all my wiring so will stick with the 8.5KWh if it turns out I would need to upgrade the wiring to get a better powered model.

Comments

  • Myser
    Myser Posts: 1,908 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    You will need to check the gauge of the existing cable and the breaker will need to be uprated appropriately if the cable can supply a higher power shower.
    If my post hasn't helped you, then don't click the 'Thanks' button! ;)
  • =rizla=
    =rizla= Posts: 220 Forumite
    As Myser says, you need to check the wiring gauge and where it is.




    http://www.gainsboroughshowers.co.uk/Site-Information/Cable-Size-Chart/
  • Ectophile
    Ectophile Posts: 8,374 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    A 9.5kW shower would just about hit the limit for a 40A fuse or breaker.

    But as others have said, you'd need to check if the cable is up to it. It can even make a difference how the cable is run. If it's covered in loft or wall insulation at some point, the cable has to be down-rated accordingly.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
  • Londoner_1
    Londoner_1 Posts: 183 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    My 9.5kw shower has 10mm2 cabling and a 32a fuse (should be 40a), however it works fine. It replaced a 10.5 kw one which used to trip for obvious reasons.

    However its on a old wylex fuse board, when fuse brd gets changed i will have it moved to the 40a mcb.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354K Banking & Borrowing
  • 254.3K Reduce Debt & Boost Income
  • 455.3K Spending & Discounts
  • 247.1K Work, Benefits & Business
  • 603.7K Mortgages, Homes & Bills
  • 178.3K Life & Family
  • 261.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.