OFCH not heating water - only luke warm
Options

BOBS
Posts: 2,871 Forumite
Comments
-
I presume by OFCH you mean Open Flue Central Heating, but we really need a better description of the system in your house and what it is doing before being able to make a helpful contribition
What type/make/model of boiler. Is it fully pumped? i.e.
do you have two 2 port zone valves or a three port? What type/make of cylinder do you have? Is the pump running, are the thermostats on your boiler/cylinder switching the pump on /off when you operate them. If the pump works have you tested for a blocked cold feed, Are the ball valves in your attic tanks operating OK when you waggle them (they can stick, particularly in the Feed/expansion tank for the central heating as it gets little use). Does the boiler carry on running or does it cut out fairly quickly when you put in on HW setting?
When did it last work properly? Has it suddenly stopped or has it been a gradual deterioration over time.
Come back to us with the bigger picture. It really helps people to give you better advice0 -
Or do you mean "Oil Fired Central Heating"?
We have had problems with the above before due the boiler needing a service, which included cleaning the heat exchanger and fitting a new burner nozzle/jet which solved the problem.0 -
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.2K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.3K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards