Central Heating noisy

Since my last British Gas Homecare visit when they replaced the pump and turned the hot water cylinder thermostat down by 5 degrees to 65 the system is permanently gurgling and the radiator bleed water is coming out more black than before.

Any idea what work would need doing to fix?

Many thanks
S

Comments

  • check the arrow on the pump body it should be pointing towards the mid pos valve, I've seen a few from BG & others that are installed the wrong way round, plus the cylinder stat should be at 60d not 65d
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • Supernova
    Supernova Posts: 732 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    check the arrow on the pump body it should be pointing towards the mid pos valve, I've seen a few from BG & others that are installed the wrong way round, plus the cylinder stat should be at 60d not 65d

    Thanks.

    Installed like this:

    Pump_zpsbe7cb72a.jpg

    Arrow on the left?
  • look at the back at the top it will have an arrow on the body inbetween the two valves
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • Supernova
    Supernova Posts: 732 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    look at the back at the top it will have an arrow on the body inbetween the two valves

    Thanks. Arrow is pointing towards the left i.e back towards the boiler. There are two valves either side of the pump.

    S
  • southcoastrgi
    southcoastrgi Posts: 6,298 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    do you have a mid position valve that directs the water from the boiler to either the heating or hot water that looks something like this ? if so where is this in relation to the pump ?

    mid_pos_valve.jpg
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • Supernova
    Supernova Posts: 732 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    do you have a mid position valve that directs the water from the boiler to either the heating or hot water that looks something like this ? if so where is this in relation to the pump ?

    mid_pos_valve.jpg

    No, nothing of that ilk near the boiler, just two normal valves either side of the pump like the one on the left at the back plus the red hot water shut-off valve further down the pipes to the right.

    Thanks
    S
  • Supernova
    Supernova Posts: 732 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    Well in the end called back British Gas because the fan was stuck and got one of the engineers who wasn't a jobsworth like the last few. He turned the pump speed down (only a small flat) and bled all the radiators with the heating off. Now perfick, heating far more efficient - and no noise!

    S
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.3K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.4K Mortgages, Homes & Bills
  • 177.1K Life & Family
  • 257.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.