Combi pressure query

Grampus8
Grampus8 Posts: 883 Forumite
Tenth Anniversary
Morning,

I had a new combi boiler installed in May. Had the heating on to test it at the time but hasn't been on since. Pressure was initially set at 1.5

Have been checking it periodically and it is currently at 1.1

As I said, we've only been using the hot water, not the heating; would this type of pressure fall be of any worry or is it relatively normal?

I had pressure issues with the last boiler hence the worry!

If someone could set my mind at rest (or not) that would be great.

Ta

Comments

  • Andy_WSM
    Andy_WSM Posts: 2,217 Forumite
    Part of the Furniture 1,000 Posts Uniform Washer Rampant Recycler
    This could be air settling out of the system (normal) or just the fact that the water around the system is cooler now, so the pressure has reduced. You will find the pressure fluctuates depending on the temperature of the system. It is designed to do this a pressure vessel is fitted to allow for expansion.
  • Grampus8
    Grampus8 Posts: 883 Forumite
    Tenth Anniversary
    Thanks Andy, so nothing to worry out?
  • No, sounds normal.

    You could top it back up to 1.5 whilst the systems cold if you wish.
  • Andy_WSM
    Andy_WSM Posts: 2,217 Forumite
    Part of the Furniture 1,000 Posts Uniform Washer Rampant Recycler
    Grampus8 wrote: »
    Thanks Andy, so nothing to worry out?

    Nothing at all to worry about. You'll probably find the manual says pressure should be set at between 1 & 1.5 bar. In which case I'd have to disagree with societys child and not top up - problem is if you top up to 1.5 bar now it's colder, it could well reach 2 bar + when it's hot.
  • Grampus8
    Grampus8 Posts: 883 Forumite
    Tenth Anniversary
    Splendid. Thanks all.
  • societys_child
    societys_child Posts: 7,110 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 10 October 2014 at 1:26PM
    Andy_WSM wrote: »
    - problem is if you top up to 1.5 bar now it's colder, it could well reach 2 bar + when it's hot.
    Yes, the instruction booklet should be consulted, only suggested topping back up to what it was originally set at by the installer ;)

    If it drops too low, it' could lock-out (mine states 1.5 and won't work when it drops below 0.5 bar)
  • Andy_WSM
    Andy_WSM Posts: 2,217 Forumite
    Part of the Furniture 1,000 Posts Uniform Washer Rampant Recycler
    Yes, the instruction booklet should be consulted, only suggested topping back up to what it was originally set at by the installer ;)

    If it drops too low, it' could lock-out (mine states 1.5 and won't work when it drops below 0.5 bar)

    That's a fair point, but I have learnt over the years to never trust the "expert". :o

    Always refer to manual. It's not normally wrong.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 348.6K Banking & Borrowing
  • 252.2K Reduce Debt & Boost Income
  • 452.5K Spending & Discounts
  • 241.3K Work, Benefits & Business
  • 617.8K Mortgages, Homes & Bills
  • 175.8K Life & Family
  • 254.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.