Boiler problems...

I've got an Alpha CB24X boiler. The pressure was showing as 0.25 on cold, below the green zone, so I topped it up til the needle reached the green.

I then turned the heating on, and the needle went crazy and shot around past 4 bars all the way to beneath 0 again so it's now obviously got too much pressure.

How can I release the pressure in the system? I tried turning off the mains water at the stop !!!! and then tried turning taps on and the needle did drop back down but the moment I turned the taps off it went back up past 4.

Help!

Comments

  • Ectophile
    Ectophile Posts: 8,305 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    The easiest way to reduce the pressure is to let some out through the bleed valve of a radiator, but if it's that high, you'd need to let quite a lot out. There also may be a little tap below the lowest radiator in the system. They normally need a square key to open.

    Double check that the filler valves at both ends of the filling loop are properly turned off.

    Really, the pressure should not be able to go above maximum (about 3 to 4 bar). There is supposed to be a pressure relief valve in the boiler to stop that happening. If it isn't working, you need to get it seen to, as it's a safety feature to stop things going bang.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
  • stevetuk
    stevetuk Posts: 123 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    Thanks for the quick reply. I tried bleeding a radiator downstairs but you're right that it wasn't dropping the pressure enough with what I got out so I think I'd have needed to bleed it for hours before it had any impact.

    For now I turned the boiler off at the mains electric supply and as I've got Homecare with British Gas I've booked an engineer to come tomorrow.

    Checking now, the pressure has dropped a bit from underneath the 0 to where I'd guess '5' would be if it was on the dial...
    I'm hoping desperately that it will keep going.

    There is an outlet pipe at the side of the house and this is dripping water outside so I wonder if that's the overflow kicking in?

    Also, the boiler itself is dripping from one of the pipes underneath. So I've put a bowl under that for overnight.

    For now, no heating or hot water :(
  • stevetuk
    stevetuk Posts: 123 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    The pressure is down to 3.5 this morning and the pipe outside is still dripping, slowly.

    I booked a BG engineer as I have Homecare 200 - will I be charged the £50 excess as a call out fee even if no work is required? Should I just cancel the appointment?

    Steve
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    It's still way over pressure, around 1 bar at cold normally. You have a leak from the PRV-now it's lifted due to over-pressure, it'll almost certainly need replacing.
    The filling loop may have a valve on each end, one end is either leaking or you failed to close it properly. All you had to do was close the other end and then bleed a rad to get the pressure back to normal.
    The other causes of the original issue are a faulty EV or a leak on the CH circuit.
    No free lunch, and no free laptop ;)
  • Lgas
    Lgas Posts: 365 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    Don't cancel the appointment, pressure still way too high, engineer needs to drain the boiler, check the air charge in the expansion vessel, and clean or replace the pressure relief valve. Possibly a leak somewhere but usually it's a flat EV - or if the engineer's unlucky, the EV needs replacing.

    I also think your filling loop is still open - check both ends of the flexible hose.
  • Lgas
    Lgas Posts: 365 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    Oops didn't see Macman's response, pretty much the same thing!
  • StuC75
    StuC75 Posts: 2,065 Forumite
    there should be a drain valve at the lowest point, that you could connect a hose pipe onto - this could be on one of the radiator feed pipes - or if you have a magna valve 'thing' that will have a valve that can be opened to drain it quick - this is best done when the heating is cold so as not to scold - plus you need the cold water pressure to be right...
  • stevetuk
    stevetuk Posts: 123 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    Lgas wrote: »
    Don't cancel the appointment, pressure still way too high, engineer needs to drain the boiler, check the air charge in the expansion vessel, and clean or replace the pressure relief valve. Possibly a leak somewhere but usually it's a flat EV - or if the engineer's unlucky, the EV needs replacing.

    I also think your filling loop is still open - check both ends of the flexible hose.

    Thanks for all the replies, really appreciate it. Kept the appointment and sure enough it was a flat EV and needed the prv and filler loop replacing. The engineer drained the system, sorted the pressure out, replaced the parts, and away we go.

    For now he's capped the filler loop ends and left the pipe on the top if I ever need to use it. Apparently it shouldn't have been left connected, although the system had been losing pressure periodically which I thought was normal, hence topping it up now and then. The flat EV was apparently why the pressure skyrocketed because I didn't fill it any more than I have done previously in one go.
    All sorted now. And my house is still standing :D
  • Ectophile
    Ectophile Posts: 8,305 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    In theory, you're always supposed to remove the filling loop once you've finished filling the system.

    Nobody ever does, though.
    If it sticks, force it.
    If it breaks, well it wasn't working right anyway.
  • Lgas
    Lgas Posts: 365 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    Excellent, glad it's sorted :)
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 353.5K Banking & Borrowing
  • 254.1K Reduce Debt & Boost Income
  • 455K Spending & Discounts
  • 246.5K Work, Benefits & Business
  • 602.8K Mortgages, Homes & Bills
  • 178K Life & Family
  • 260.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.