Devastated by EDF Bill
Comments
-
Look the water controller - controls, boost is only on when the boost [top heating element] light is lit [terminal 4 & 5 can not be simultaneously live] regardless of where your switches are positioned. Both E7 timed [bottom heating element] and boost can not be on together the controller won't allow it. E7 or boost is indicated by a lit neon.
The 2 things you need to clarify is that you are on E7 and not E10, and that you have a dual element PartL water cylinder with 2 distinct sets of wiring coming from the controller, one set going to the bottom [off peak] element and the other going to the top [on peak] heating element.Disclaimer : Everything I write on this forum is my opinion. I try to be an even-handed poster and accept that you at times may not agree with these opinions or how I choose to express them, this is not my problem. The Disabled : If years cannot be added to their lives, at least life can be added to their years - Alf Morris - ℜ0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.2K Banking & Borrowing
- 253.6K Reduce Debt & Boost Income
- 454.3K Spending & Discounts
- 245.3K Work, Benefits & Business
- 600.9K Mortgages, Homes & Bills
- 177.5K Life & Family
- 259.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards