"Dedicated cooker circuit with a 32/40 amp MCB"?

What does this actually mean?

We are purchasing a house (have exchanged, but don't complete until next month). There is a dual fuel range cooker in place and we want to replace with induction.

The electrical installation certificate states that there is a cooker circuit (that only serves that cooker). The Overcurrent Protective Device has a 32A rating.

Would this fulfill the requirement of "a dedicated cooker circuit with a 32/40 amp miniature circuit breaker"? Would we be wiser to upgrade the MCB to a 40 amp? Is that straightforward?

QT
«1

Comments

  • lee111s
    lee111s Posts: 2,987 Forumite
    Eighth Anniversary 1,000 Posts Combo Breaker
    I had a similar issue. Previously had a gas oven and electric hob. Since changing to an Induction I had to convert the double socket that was protected by the 40a fuse into a single cooker style outlet using 2.5mm twin and earth cable solely for the induction hob purely because of how much current it can potentially draw (7.2Kw). I then ran a spur from another socket to create a single standard socket for my new oven.
  • Ben84
    Ben84 Posts: 3,069 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    edited 21 February 2014 at 2:55PM
    If the manual suggests a 32A circuit, which is what you have, and your electrician is happy with the condition and quality of the circuit, you should be fine.

    It looks more confusing than it is, but the amp rating of the cooker doesn't have to match the amp rating of the supply. In practice it rarely does. The sizing of cooker circuits is treated differently to just about any other appliance I can think of, and many electric cookers are connected to lower amp circuits than their rating due to diversity - basically they assume nobody will turn on every element at once. I believe the calculation is that the supply must match the first 10A of the cooker's rating plus 30% of the remainder and 5A if you have a socket on the circuit (can be removed if needed to gain back the 5A). Presumably, as a 32A supply is recommended, your cooker falls within the range of a 32A supply when diversity is calculated.
  • lee111s wrote: »
    I had a similar issue. Previously had a gas oven and electric hob. Since changing to an Induction I had to convert the double socket that was protected by the 40a fuse into a single cooker style outlet using 2.5mm twin and earth cable solely for the induction hob purely because of how much current it can potentially draw (7.2Kw). I then ran a spur from another socket to create a single standard socket for my new oven.


    Are you sure 2.5mm is big enough?
  • lee111s
    lee111s Posts: 2,987 Forumite
    Eighth Anniversary 1,000 Posts Combo Breaker
    My qualified electrician installed it so I'd imagine so.
  • lee111s wrote: »
    My qualified electrician installed it so I'd imagine so.




    Seems small, I hope he got his maths right when he did it.
  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    2.5mm is no where near big enough to cope with a load of 7.2Kw - I kid you not THAT IS A SEVERE FIRE RISK

    2.5 mm is roughly rated to 20 A max on a radial circuit.

    I would have put a 6mm cable in for a cooker circuit - always have done always will do as that has always been the norm.

    DO NOT USE YOUR COOKER UNTIL THE CABLE SIZE HAS BEEN CHECKED.
    You may click thanks if you found my advice useful
  • 2.5mm is not big enough!
    The fuse/mcb protects the cable not the appliance
  • lee111s
    lee111s Posts: 2,987 Forumite
    Eighth Anniversary 1,000 Posts Combo Breaker
    Aplogies, read through my texts and it was indeed a 6mm twin and earth he had me get so that's what fitted.
  • QTPie
    QTPie Posts: 1,373 Forumite
    Thanks very much.

    So cooker requires a 32A dedicated circuit and has an electrical load of 11.7kW.

    I have a 6mm dedicated cooker circuit (6mm live, 4mm CPC) with 32A MCB. This should be sufficient and safe? Even for 11.7kW?

    Thanks
  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    edited 22 February 2014 at 10:20PM
    QTPie wrote: »
    Thanks very much.

    So cooker requires a 32A dedicated circuit and has an electrical load of 11.7kW.

    I have a 6mm dedicated cooker circuit (6mm live, 4mm CPC) with 32A MCB. This should be sufficient and safe? Even for 11.7kW?

    Thanks

    NO ! 6 mm rated to roughly 8.5Kw 46A max if clipped direct.
    11.7Kw you need to upgrade the wiring to 10mm might even be 16mm and the MCB to 50A

    11700 / 240 = 48.75A which is over the max rating for 6mm cable

    Use that cooker on full load and kiss goodbye to your home !
    You may click thanks if you found my advice useful
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243K Work, Benefits & Business
  • 619.9K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.