📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!

Electrical Question

I have noticed that the consumer unit in the house has 16A MCB for the garage circuit.
The CU in the garage has a 32A MCB for the sockets.
Both are on RCD.
Should they both have the same rated MCBs ? and is there any issue with two RCDs?
I would be grateful for advice.
Forgotten but not gone.

Comments

  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    A bit of bad design there !

    Do you know what size of cable it is that supplies the garage ? that will dictate what size MCB should be being used to supply the garage board.

    As for the RCD's again bad design to have two on one circuit - completely unnecessary. If you have one on the consumer unit then that protects the whole installation including the wiring to the garage.
    You may click thanks if you found my advice useful
  • ValHaller
    ValHaller Posts: 5,212 Forumite
    1,000 Posts Combo Breaker
    Whoever did that had not a clue about circuit discrimination - the idea that the protective device which protects the most downstream part of the installation towards the fault should be the one to blow.

    The 32A MCB for the garage will never blow, of course, so going on what MB says, all cabling to and in the garage should be adequate for a 16A breaker.

    On the RCDs, regardless of current rating ordinary RCD's do not discriminate in any meaningful sense. Even if you have a 100mA RCD feeding a 30mA RCD, any earth fault is likely to exceed 100mA, so both or either could trip.

    You can have RCD's in series so that they discriminate, but the upstream one has to be a time delay RCD, which allows 100ms for the downstream RCD to trip. This obviously reduces the protection given to circuits only protected by the upstream RCD and is not good if one of those circuits is feeding an electric lawnmower for example.
    You might as well ask the Wizard of Oz to give you a big number as pay a Credit Referencing Agency for a so-called 'credit-score'
  • tony6403
    tony6403 Posts: 1,257 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    Thanks for the very helpful replies . It's a 2.5mm cable.
    Forgotten but not gone.
  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    Ideally then dependent upon length of cable etc you want a 20A MCB at your consumer unit, then in the garage the 32A one wants down rating to 16A that way giving you correct discrimination.

    As for the RCD's I would leave them as they are unless they prove to be a PITA if they trip, at least with the correct ratings set up any short circuit or over current in the garage will trip that MCB and hopefully the RCD in there as well. Only time will tell.
    You may click thanks if you found my advice useful
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.7K Banking & Borrowing
  • 253.4K Reduce Debt & Boost Income
  • 454K Spending & Discounts
  • 244.7K Work, Benefits & Business
  • 600.1K Mortgages, Homes & Bills
  • 177.3K Life & Family
  • 258.3K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.