Electric shower

2»

Comments

  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Since all we know about the cabling is that it's a 'thick grey one', we don't even know if the existing cable and circuit protection is adequate for a 7Kw shower. By all means get a higher rated unit (7or 8kW is going to give a pretty miserable flow rate in anything but warm weather), but get the circuit uprated and RCD protected at the same time. The extra cost is not that great if the sparky is attending anyway.
    There's no legal requirement to fit an RCD, but it would be foolish in the extreme not to have such protection on a shower circuit.
    No free lunch, and no free laptop ;)
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.4K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.3K Work, Benefits & Business
  • 604K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.