Problem with Boiler

Over the last few days a problem has developed with my boiler. There seems to be 2 things at play:

1) The boiler switches on seemingly randomly when there is no demand for water from the programmer. When this happens the "burner" light is lit or flashing and the pump next to the hot water cylinder is on.

2) Occasionally, a reasonably loud grinding/banging sound can be heard from the boiler which lasts about 20-30 seconds.

What sort of problem could this be? Are there any simple fixes? If not, how expensive is this likely to be to fix?

The boiler is an Ideal icos HE18, if any more detail is required, please say so.

Thanks
«1

Comments

  • gas4you
    gas4you Posts: 2,602 Forumite
    Check any heating/hot water zone valves first.
  • southcoastrgi
    southcoastrgi Posts: 6,298 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    D
    you are being too kind not even metioning the "I" word :D
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • fireice
    fireice Posts: 120 Forumite
    Part of the Furniture 10 Posts Combo Breaker
    edited 3 July 2013 at 8:09PM
    gas4you wrote: »
    Check any heating/hot water zone valves first.

    Are these what you are talking about? How do you check that they are the problem? (I have zero knowledge about boliers and plumbing!)

    Thanks
  • moneysaver
    moneysaver Posts: 836 Forumite
    Part of the Furniture 500 Posts Name Dropper
    fireice wrote: »
    Over the last few days a problem has developed with my boiler. There seems to be 2 things at play:

    1) The boiler switches on seemingly randomly when there is no demand for water from the programmer. When this happens the "burner" light is lit or flashing and the pump next to the hot water cylinder is on.

    2) Occasionally, a reasonably loud grinding/banging sound can be heard from the boiler which lasts about 20-30 seconds.

    What sort of problem could this be? Are there any simple fixes? If not, how expensive is this likely to be to fix?

    The boiler is an Ideal icos HE18, if any more detail is required, please say so.

    Thanks


    Has your boiler got a pre heat function? Check the manual for this & switch if off if not needed.

    That could be your number 1 question answered.

    Question 2 could also be linked to this.

    I am only guessing as I am not an engineer.



    Moneysaver
  • Myser
    Myser Posts: 1,907 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    fireice wrote: »
    Are these what you are talking about?

    Your link doesn't seem to work for some reason?

    Here are a couple of examples of zone valves:

    reliance-2-port-motorized-zone-valve-22mm.jpg

    valves-new.jpg
    If my post hasn't helped you, then don't click the 'Thanks' button! ;)
  • fireice
    fireice Posts: 120 Forumite
    Part of the Furniture 10 Posts Combo Breaker
    Yes, they were what I was linking to (I've edited the link now, sorry). How do I check if these are the problem?

    The boiler does not have a preheat function, I think these are only on combi boilers. The banging sound is too loud to be normal.
  • Myser
    Myser Posts: 1,907 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Check to see if they are stuck i.e. partially closed. You can do this by setting the programmer to off for both heating and hot water then remove the valve actuator heads (metal/plastic block).

    If the valve is partially closed, a small microswitch inside the actuator head may be causing the boiler to randomly fire. You will know if the valve is not fully closed as the valve body spindle won't be completely horizontal or vertical i.e. between 9 and 3 or 12 and 6 on a clockface .
    If my post hasn't helped you, then don't click the 'Thanks' button! ;)
  • fireice
    fireice Posts: 120 Forumite
    Part of the Furniture 10 Posts Combo Breaker
    Would the system need to be drained first?

    I don't really feel confident about trying to fix stuff related to plumbing (don't want to flood the house!). Does anyone have any recommendations on how to find a good plumber and roughly how much this should cost to fix?
  • Myser
    Myser Posts: 1,907 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    fireice wrote: »
    Would the system need to be drained first?

    I don't really feel confident about trying to fix stuff related to plumbing (don't want to flood the house!). Does anyone have any recommendations on how to find a good plumber and roughly how much this should cost to fix?

    No the system would not need to be drained, you just remove the valve actuator head.

    If you don't feel too confident, perhaps ask friends/relatives for recommendations of Gas Safe Registered people. Otherwise, you can search the Gas Safe Register.
    If my post hasn't helped you, then don't click the 'Thanks' button! ;)
  • The boiler will/should only ignite if there is a heat demand. This comes from the hot-water storage thermostat, or the CH thermostat. The pump runs for two reasons, 1) there is a heat demand, and 2) the boiler case is hot, then it circulates water through the boiler to cool it down. Any crashing/banging/thumping sounds are probably due to air in the system, which will need bleeding away. There should be a bleed screw on the hot-water cylinder feed from the boiler, and on the radiators. Some heating engineers fit them to the boiler as well, but a lot of plumbers rely on the air bubbles finding their way back up the boiler cold supply pipe
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.2K Banking & Borrowing
  • 252.8K Reduce Debt & Boost Income
  • 453.2K Spending & Discounts
  • 243.2K Work, Benefits & Business
  • 597.6K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 256.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.