We’d like to remind Forumites to please avoid political debate on the Forum.

This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.

📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
The Forum now has a brand new text editor, adding a bunch of handy features to use when creating posts. Read more in our how-to guide

Mira Go 10.8kw shower.

I want to upgrade my shower and my question is about my present electrics. The cable is 6mm, not enclosed,and the breaker in the box says B.40. Will this be ok for the new shower?? thanks for any advice.

Comments

  • southcoastrgi
    southcoastrgi Posts: 6,298 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    no for both, that size shower will req a 10mm cable & a 45amp "breaker"
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • almeria1
    almeria1 Posts: 132 Forumite
    Thanks for that so I have a follow up question as you would expect. Could you give me an indication of the cost of changing the cable and the breaker,ta. I live in southern england just in case regional charges vary.
  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    It depends on how much cable is required and whether a rcbo can be fitted into you existing fuse board.

    10mm cable aint cheap neither are rcbo's !
    You may click thanks if you found my advice useful
  • retepetsir
    retepetsir Posts: 1,238 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    almeria1 wrote: »
    Thanks for that so I have a follow up question as you would expect. Could you give me an indication of the cost of changing the cable and the breaker,ta. I live in southern england just in case regional charges vary.

    It depends on the length and route of cable, etc, etc.

    The Great Declutter Challenge - £876 :)

  • almeria1
    almeria1 Posts: 132 Forumite
    Had a sparks round to look at the job. Apart from the fact that he said the existing cable and breaker would probably be ok -which I will not accept - he then said the job would entail lifting the landing carpet,floorboards etc. I must admit I thought that the 10mm cable could be attached to the 6mm cable and pulled through. The sparks said no that could not be done. So do all the electricians on the site agree with him. I just want to be sure as she who must be obeyed is not to happy with his claim but if we are going to have the new shower fitted I guess needs must.
  • muckybutt
    muckybutt Posts: 3,761 Forumite
    Part of the Furniture Combo Breaker
    almeria1 wrote: »
    Had a sparks round to look at the job. Apart from the fact that he said the existing cable and breaker would probably be ok -which I will not accept -.

    :eek: most certainly is not ok to use that cable on that size load

    10.5kW / 45.65A so a 40 A mcb is not correct size either, cable has to be minimum 10.0mm. Your electrician sounds incompetent to say the least.

    If the cable needs replacing you will need it signed off by a registered electrician, jobs like this cant be done by any tom-!!!!!! or harry like the electrician you have had around sounds like.

    How many meters back to your fuse box and what is the make of your fuse box ?
    You may click thanks if you found my advice useful
  • almeria1
    almeria1 Posts: 132 Forumite
    Had a look and it is a MK make fitted Jan 2010. At a really rough guess a cable run of 15 metres.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.2K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.3K Spending & Discounts
  • 247.2K Work, Benefits & Business
  • 603.8K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.