Heating causes boiler to trip and blow the fuse

I have an annoying problem that started yesterday out of the blue

If I put my boiler on, to heat hot water, it works fine

But as soon as I start the heating by turning up the thermostat, it trips the boiler in the fuse box and also blows the 3a fuse where the boiler is wired into the wall?

Anything I can check before calling someone in?

Thanks
Andrew

Comments

  • CrazyRed
    CrazyRed Posts: 254 Forumite
    The only thing different about a boiler heating hot water and a boiler heating the heating circuit is the pump.

    First thing I'd look at is the pump and see if it's seized - this would cause an overload and the fuse to blow.
    PLEASE NOTE:

    I limit myself to responding to threads where I feel I have enough knowledge to make a useful contribution. My advice (and indeed any advice on this type of forum) should only be seen as a pointer to something you may wish to investigate further. Never act on any forum advice without confirmation from an accountable source.
  • shaun_from_Africa
    shaun_from_Africa Posts: 12,858 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    edited 30 December 2012 at 1:47PM
    CrazyRed wrote: »
    The only thing different about a boiler heating hot water and a boiler heating the heating circuit is the pump.

    It is highly likely that the heating system in question uses the pump for both heating and hot water as this is still the most common setup there is.

    It is far more probable that the fault is with the motorised valve seized up in the "hot water only" position and it is this causing the fuse to blow when it tries to motor to the heating position.

    512px-Y-Plan-Water.gif
  • Fatman
    Fatman Posts: 69 Forumite
    Part of the Furniture Combo Breaker
    Th boiler is about 12 years old if it makes a difference.

    How would I see the pump or this motorised valve?
  • shaun_from_Africa
    shaun_from_Africa Posts: 12,858 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    edited 30 December 2012 at 10:11PM
    The age of the boiler won't have any relevance on the problem as it is simply a heater and doen't know where the hot water is going.
    If the boiler was at fault and blowing the fuse for heating then it would do the same for hot water.

    The pump and valve are normally located close to each other and may well be in your loft.
    This webpage gives a few examples of what it may look like.
    http://images.google.com/search?tbm=isch&hl=en&source=hp&q=central+heating+motorised+valve&gbv=2
    They are often in two parts, the mechanical valve and the electrical actuator and the two parts can sometimes be pulled apart.

    If you can do this (don't try it if you are not confident with what you are doing), you will be able to detemine whether it is an electrical problem with the actuator of if the mechanical part of the valve is jammed in one position.
    Simply take the electrical actuator off the valve assy and switch the heating on again.

    If the boiler starts up and the fuse doesn't blow then it will be the mechanical part of the valve jammed and this will need to be replaced.
    If the fuse blows then it will be the electrical actuator or the wiring between it and the central heating controller.

    One other possibility is the thermostat or the wiring to it, but my gut instinct would be the valve.
  • Fatman
    Fatman Posts: 69 Forumite
    Part of the Furniture Combo Breaker
    Turns out I have 2 separate pumps. One for CH and one for HW.

    The CH pump appears to be broken, ill be replacing it on Wednesday!

    Thanks for all your help.
  • barose
    barose Posts: 10 Forumite
    My system today started blowing the 5 amp boiler circuit breaker. I tried several things but noted that the fuse blew even with the thermostat turned down (off). So with thermostat off the boiler isolation switch on and pulling the heating timer control on - fuse blows. With the heating timer control 'off'' and the hot water timer control 'on' the boiler runs fine. I tried disconnecting the pump live wire, no difference and unplugging the boiler, no difference. Seems as soon as the heating timer control lever is moved - pop.

    Could really use some advice on where to look.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243K Work, Benefits & Business
  • 619.9K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 255.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.