Adding Another Radiator
Ms_Chocaholic
Posts: 12,855 Forumite
Hi
I have a conservatory leading from my dining room, the radiator in my dining room is about 2 feet from the outside wall where my conservatory starts. Does anyone know how easy it would be to get an additional radiator added.
Just to add that between the radiator and the wall, in the floor, is some pipework with a screw that you turn if you want to drain the system. Wanted to mention this in case it made a difference.
Thanks
Ms C x
I have a conservatory leading from my dining room, the radiator in my dining room is about 2 feet from the outside wall where my conservatory starts. Does anyone know how easy it would be to get an additional radiator added.
Just to add that between the radiator and the wall, in the floor, is some pipework with a screw that you turn if you want to drain the system. Wanted to mention this in case it made a difference.
Thanks
Ms C x
Thrifty Till 50 Then Spend Till the End
You can please some of the people some of the time, all of the people some of the time, some of the people all of the time but you can never please all of the people all of the time
You can please some of the people some of the time, all of the people some of the time, some of the people all of the time but you can never please all of the people all of the time
0
Comments
-
Depends on the way the system is currently piped. Microbore will usually only supply 1 radiator per loop from the manifold. 15mm will be borderline, 22mm will probably do depending on what else is on that loop.
To comply with Building Regulations, the radiator in the conservatory should be on a separate zone so it is only used when required.A kind word lasts a minute, a skelped erse is sair for a day.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.5K Banking & Borrowing
- 253.7K Reduce Debt & Boost Income
- 454.5K Spending & Discounts
- 245.5K Work, Benefits & Business
- 601.4K Mortgages, Homes & Bills
- 177.6K Life & Family
- 259.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards