Twisted or not doesn't really matter, what is critically important is that all conductors are firmly clamped at the connection point with a minimal amount of exposed copper
Twisting as described in # 19 is a recipe for disaster, twisting as described in #18 is fine and might even have advantages0 -
I didnt say they shouldnt be put in singularly ! that is how they should be.
As for twisting the wires takes up more room ? thats ridiculous ! the wires dont grow thicker lol and the individual wires will still be the same cross sectional area.
This is one reason part p was bought in dodgy diyers thinking they are sparkies.
Follow my or dsvardy's advice.
Also, since the 3 straight ones are not held together they may be coaxed to fit into an oblong hole differently, whereas 3 twisted ones won't. So obviously whether the hole is circular or oblong makes a difference.
You need to be able to understand a bit of mathematics and to visualize shapes to understand that sort of thing.0 -
Twisted or not doesn't really matter, what is critically important is that all conductors are firmly clamped at the connection point with a minimal amount of exposed copper
Twisting as described in # 19 is a recipe for disaster, twisting as described in #18 is fine and might even have advantages
One of the properties of copper is that it hardens as you work it. It comes off the reel 'annealed' - ie in a soft state. A twist which work hardens it a bit means that the copper does not retreat from the clamping screw over the first day or so, because of a small degree of work hardening. Working it with a corkscrew twsit means that you have very hard copper next to ve'y soft copper an no graduation in hardness. It tends to break at the first soft copper adjacent to the work hardened copper.Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam0 -
5 years of a City and Guilds 236 Part 1 and Part 2 wasted, I should have come on here and did a distance learning course.
How many 2.5 mm cables allowed in to a 25 mm metal conduit located in an aviation fuel depot?
Half as many as the number of jackhammers allowed to be tested in a nitroglycerine store
Seriously though, thanks for the advice and no I won't twist them.Solar install June 2022, Bath
4.8 kW array, Growatt SPH5000 inverter, 1x Seplos Mason 280L V3 battery 15.2 kWh.
SSW roof. ~22° pitch, BISF house. 12 x 400W Hyundai panels0 -
The wrapping wires around the lower part of one wire and then inserting the single wire into the connector is dangerous beyond belief.
Not only is there arcing/shock hazards but also you are now asking the CSA of one core to take the current of the other two as well.
So instead of each 2.5mm² taking the current to the connector, potentially 13amps, you are asking one 2.5mm² core to take potentially 39amps.0 -
The wrapping wires around the lower part of one wire and then inserting the single wire into the connector is dangerous beyond belief.
Cheers.The difference between genius and stupidity is that genius has it's limits. - Einstein0 -
For what it's worth, I was taught never to twist cables togeter. One of the main reasons: If the CPC's on a ring final have been twisted together, then for some reason come away from the terminal, you will still get an end to end reading, but no earth connection at the socket. Of course, other tests should pick up the problem, so long as testing is being carried out at each socket.0
-
Agreed, likewise if one of the other conductors becomes disconnected then youd end up with two radial circuits as opposed to one ring final and as electricity takes the path of least resistance then flows exceeding 16amps could be sent down one radial which would exceed the regs.0
-
red alert, condition red!
do not use this dangerous method. I tried it and now my house is burned down. 20 fire tenders attended the fire. Now i am homeless.“Learn from the mistakes of others. You can never live long enough to make them all yourself.”
― Groucho Marx0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.1K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599K Mortgages, Homes & Bills
- 177K Life & Family
- 257.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards