Conventional pumped system. Hot water OK but no central heating
tired_dad
Posts: 641 Forumite
Have a conventional boiler in utility. Hot water storage upstairs, CWS in loft. Pumped system with a valve ( not sure about the 2 or 3 way side of things, but there are 3 pipes going into the valve).
There is a old programmer ( slider for hot water and heating with options for "off, once, twice, continuous").
Problem: hot water working with no problems. Boiler fires up no problem. However, no heating. The programmer lights up OK as if it's functioning. The CH pump remains silent and the boiler does not fire up).
It's a grundflos pump.
Would value advice ESP at making a diagnosis.
TIA
There is a old programmer ( slider for hot water and heating with options for "off, once, twice, continuous").
Problem: hot water working with no problems. Boiler fires up no problem. However, no heating. The programmer lights up OK as if it's functioning. The CH pump remains silent and the boiler does not fire up).
It's a grundflos pump.
Would value advice ESP at making a diagnosis.
TIA
0
Comments
-
Is there a room thermostat for the heating?
If not I suspect the programmer has partially died given that the wiring to the boiler is obviously fine (otherwise no hot water).
If there is a thermostat that may have died, or a cable is loose between it and the programmer.
the good news is, that a new programmer is only about £30-50 so if it is that it's a fairly cheap fix.0 -
No room thermostat, just an old dial on the boiler itself.
There is a long probe that is sited at the top of the firing chamber. It fits into a hole into the chamber. Not sure what that is0 -
Do the radiators get hot if the water is on?
If not, sounds like the actuator head of the three way valve has broken.
Most can have the head replaced, but a few of the older ones need the complete valve changing.0 -
Yep, it was the 3 way valve. 28 mm fittings. New one going in as we speak0
-
For this type of system you will need the following to work [as an approximate guide]
- Programmer to provide supply when CH called for
- Roomstat to call for heating [set room stat to max]
- Divertor Valve to drive to CH position
- Pump to work
Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 354.4K Banking & Borrowing
- 254.4K Reduce Debt & Boost Income
- 455.4K Spending & Discounts
- 247.3K Work, Benefits & Business
- 604K Mortgages, Homes & Bills
- 178.4K Life & Family
- 261.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards