Can't get any pressure in our heating system

2»

Comments

  • mikey72
    mikey72 Posts: 14,680 Forumite
    Can you get a close up of the top of the exspansion vessel, and the filling loop?
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    edited 3 May 2012 at 8:36AM
    Hi: are you opening the valve at the end of this arrow with a screwdriver?

    A similar set up to this . Move the cursor/hand over the thumbnail photos and you'll see the ballofix end.

    The slot in line with the pipe means the valve is fully open. Open the ballofix valve first, then the lever end gently , pressure will rise quite quickly Turn both ends off. Take off the hose.

    GSR
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • gas4you
    gas4you Posts: 2,602 Forumite
    What is the other expansion vessel for?
  • TEssery
    TEssery Posts: 43 Forumite
    gas4you wrote: »
    What is the other expansion vessel for?

    That's for our hot water system, which is on a separate boiler.
    TRC :)
  • TEssery
    TEssery Posts: 43 Forumite
    @GSR/Canucklehead
    Ah, you may be onto something there! We thought that as there was only one tap, that was the only thing we should open. (Our other expansion vessel, for the hot water system, has two levers/taps and we open both to pressurise it). At work now, but will follow your advice at home tonight and see what happens. Fingers crossed! And thanks again for all your help :-)
    Best wishes, Tracey
    TRC :)
  • gas4you
    gas4you Posts: 2,602 Forumite
    TEssery wrote: »
    That's for our hot water system, which is on a separate boiler.

    In that case it is the wrong type of expansion vessel.

    Expansion vessels suitable for use on an unvented hot water system are always colour coded white/cream.

    Red ones are for heating systems only.
  • TEssery
    TEssery Posts: 43 Forumite
    Thank you so much for all your help. The very detailed instructions given by Canucklehead fixed the problem - system is now running and the house is toasty (but not too toasty - we're moneysavers after all!).
    Gas4you - my previous answer was not as detailed as it should be, the heated towel rails and the hot water are run off one boiler and the other radiators off the other.
    I'm chuffed to be part of a community that gives so generously of its time and expertise.
    Thanks again.
    Tracey
    TRC :)
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi: excellent news...happy to help.;)

    GSR
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.4K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.3K Work, Benefits & Business
  • 604K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.