Baxi 105e combi boiler; switches on by itself

twigtv
Posts: 2 Newbie
Anyone know what could be causing the above problem please?
The boiler fires up by itself randomly several times a day for around 15 mins then switches off again. This even happens with the timer and thermostat disconnected and in C/H or DHW mode.
The only lights lit on the control panel when the boiler comes on are the burner on & power on light. (No DHW or C/H lights)
This causes the radiators to warm up (even in summer) and must be adversly affecting my gas bill. Its been happening since last summer.
If I turn the power off & on again or turn a hot tap on and off again the boiler will shut down for a period until the same thing repeats again.
The boiler works perfectly in all other respects giving me a warm home and hot water when needed (but also when not needed:(). I have replaced the main pcb as I thought the frost sensor may have been the problem but there was no change.
I noticed that someone else had posted the same fault on another forum but no cure had been found. The boiler is around 8 yrs old so if no cure can be found it looks like a replacement boiler is on the cards.
I was going to drown my sorrows but unfortunately they've learnt to swim.
The boiler fires up by itself randomly several times a day for around 15 mins then switches off again. This even happens with the timer and thermostat disconnected and in C/H or DHW mode.
The only lights lit on the control panel when the boiler comes on are the burner on & power on light. (No DHW or C/H lights)
This causes the radiators to warm up (even in summer) and must be adversly affecting my gas bill. Its been happening since last summer.
If I turn the power off & on again or turn a hot tap on and off again the boiler will shut down for a period until the same thing repeats again.
The boiler works perfectly in all other respects giving me a warm home and hot water when needed (but also when not needed:(). I have replaced the main pcb as I thought the frost sensor may have been the problem but there was no change.
I noticed that someone else had posted the same fault on another forum but no cure had been found. The boiler is around 8 yrs old so if no cure can be found it looks like a replacement boiler is on the cards.
I was going to drown my sorrows but unfortunately they've learnt to swim.
0
Comments
-
My programmer switches on the boiler every day at mid-day to stop the pump sticking over the summer. But only for a few seconds-not 15 mins.
The frost 'stat should only activate if the flow temp drops to 5C.No free lunch, and no free laptop0 -
Finally sorted the problem of my boiler switching on by itself.
The C/H temperature sensor was the cause of the problem.
(Located on the vertical LH pipe - no need to drain anything to change it)
Firstly I swapped the 2 sensors over (C/H & DHW) expecting a different fault to happen if one of them was faulty. However, the boiler now behaved perfectly! As DHW sensor looked corroded I replaced it with a new one (after putting back the C/H one). Back to fault conditions! So then replaced the good looking C/H sensor and all now ok. Don't know what was up with it as comparing the resistance with the 2 good ones proved inconclusive.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 349.8K Banking & Borrowing
- 252.6K Reduce Debt & Boost Income
- 453K Spending & Discounts
- 242.8K Work, Benefits & Business
- 619.6K Mortgages, Homes & Bills
- 176.4K Life & Family
- 255.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 15.1K Coronavirus Support Boards