We’d like to remind Forumites to please avoid political debate on the Forum.
This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
Boiler refill too often

User2050
Posts: 20 Forumite
I had a Vaillant ecoTech boiler installed 9 months ago.
I just realised that it seems I have to refill the system too frequently, to keep the water pressure above the minimum requirement.
It is about every two months before I need to refill it again using the refill loop.
Is it normal? I was expecting something like 6 months.
I have checked all my radiators and there is no leakage. Could it be there is leakage inside the boiler (though Vailant has a good reputation according to many people)?
Has anyone experience similar problems before? How to check if there is leaking inside the boiler?
Thanks guys
I just realised that it seems I have to refill the system too frequently, to keep the water pressure above the minimum requirement.
It is about every two months before I need to refill it again using the refill loop.
Is it normal? I was expecting something like 6 months.
I have checked all my radiators and there is no leakage. Could it be there is leakage inside the boiler (though Vailant has a good reputation according to many people)?
Has anyone experience similar problems before? How to check if there is leaking inside the boiler?
Thanks guys
0
Comments
-
I had a Vaillant ecoTech boiler installed 9 months ago.
I just realised that it seems I have to refill the system too frequently, to keep the water pressure above the minimum requirement.
It is about every two months before I need to refill it again using the refill loop.
Is it normal? I was expecting something like 6 months.
I have checked all my radiators and there is no leakage. Could it be there is leakage inside the boiler (though Vailant has a good reputation according to many people)?
Has anyone experience similar problems before? How to check if there is leaking inside the boiler?
Thanks guys
Hi: call your installer.
CanuckleheadAsk to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)0 -
Either a leak on the CH circuit (not necessarily on a rad) or a sticking PRV pipe-have you checked outside for a discharge from the PRV overfow pipe?
But since it's under warranty, do as Canucklehead advises.No free lunch, and no free laptop0 -
Re-pressurising should be at least six months to a year apart.
If you turn off the isolating valves at the boiler for the flow and return pipes for the CH, if there is no pressure drop then the leak is not within the boiler. As you are topping up every two months, the pressure drop over a week is very small. Try this in the summer when the CH system can be left turned off.
More likely cause is the pressure release valve ( or safety valve) not seating properly. There is a twist knob on top which can be used to open then close this valve.
However as this is still within warranty, get the installer back.0 -
I haven't had to re-pressurise my system since it was installed 18 months ago, you have a problem!0
-
To check if it's the PRV letting by tape a sandwich bag over the end of the discharge pipe and after a week see if it's filling with water, if it is....there is your problem. But as said above, call your engineer.Lightbulb Moment 17/09/20060
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.7K Banking & Borrowing
- 253.4K Reduce Debt & Boost Income
- 454K Spending & Discounts
- 244.7K Work, Benefits & Business
- 600.1K Mortgages, Homes & Bills
- 177.3K Life & Family
- 258.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards