Swimming Pool ASHPs

Options
Casper55
Casper55 Posts: 50 Forumite
edited 16 November 2011 at 12:48PM in Green & ethical MoneySaving
Hello All
I have just spent a few hours reading MSE threads on ASHPs and get the idea that they should not be used to replace domestic gas boilers. I have read that the COP of condensing gas boilers can be as high as 2.3 . manufactures of swimming pool type heat pumps are claiming a COP of 3 or even 4. My interest in swimming pool type heat pumps is purely as a replacment of a boiler for heating a koi pond which heats water to a much lower temp of 10 to 25 deg ,much lower than a swimming pool and therefore I understand this would increaqse the efficiency of a ASHP. I am currently payiing 3.4p per kwh for gas as apposed to 10p for electricity. comparing COP for a condensing boilerof 2.3 and a ASHP of 4. the boiler comes out at the cheaper option.People thoughts on my conclusions would be appreciated, especially anyone who has experience of these types of heat pumps. Best Regards casper

Comments

  • rogerblack
    rogerblack Posts: 9,446 Forumite
    Umm - no.
    COP of condensing gas boilers would be around 0.8, if they were measured that way, which they're not.

    That is - for every 10kWh of gas you put in, you get 8kWh out of heat.
    A COP of 2.3 would mean for every 10kWh of gas that went in, 23kWh of heat came out!

    So, for each kWh of heat, you are paying around 4p.
    With an ASHP with a COP of 3 (regrettably it drops in cold weather), you'd be paying 10/3 = 3.33p, or 2.5 if you assume 4.
  • Roger black
    Thanks for the reply. Please point me to your resource where condensing bolier have a COP of 0.8. If it was so low then why arn,t more sites recommending switching which they don,t.including the energy saving trust. Here is a link that states the break even COP is 2.3. I therefore assumed this was the cop for a condensing boiler and therfore anymore than this you are making a saving
    http://www.reuk.co.uk/Compare-Heat-Pump-to-Condensing-Boiler.htm
    Please explain how a boiler is measured. My boiler has an output of 23kw . How do I measure the input other than how much gas it burns. Sorry if these are stupin questions and I am reading it all wrong. Using your figures and COPs I am paying 3.4p for every kw of heat by gas & 3.33p for kw of elecrticity for heat pump that is assuming that the heat pump has a cop of 4. A tad optimisic I believe.
  • rogerblack
    rogerblack Posts: 9,446 Forumite
    Casper55 wrote: »
    Here is a link that states the break even COP is 2.3. I therefore assumed this was the cop for a condensing boiler and therfore anymore than this you are making a saving

    It's not.
    That is the COP at which a heatpump and a gas boiler cost the same to run.

    The reason why a gas boiler, and a heatpump are comparable, despite the 'COP' of the gas boiler being 0.8, and the heatpump being 2.3, is that the gas is about 3 times cheaper.

    COP - coefficient of performance is a simple ratio of power in versus power out.
    For a gas boiler, or most normal heaters, this is under, or equal to one. (and is a figure almost never used)
    For a heatpump, it's over one.

    The input energy of your gas boiler would be found by reading your meter, and looking up the conversion table to go from units to kWh.
    The boiler will produce 23kW of heat, but it will use (perhaps) 26kW of gas.

    If you have a heatpump with a COP of 4, it produces 4* the heat compared to electricity in.
    If you're paying 10p/unit, then you'd pay 10p/4 = 2.5p per kWh.
  • Roger black Thanks for taking the time to explain that. It all makes sense now. So looking at this link the bigger unit the higher the cop for the same operating temperature http://www.cheshire.luxurypools.co.uk/crystalclear_heater_pumps/Heater_pump_Specs_and_RRP.pdf
  • rogerblack
    rogerblack Posts: 9,446 Forumite
    Read across the table.
    For example - the line 'air 8C, pool 27C' - you get for the various sizes
    3.8 3.7 3.6 3.7 3.5 3.6 3.6 3.6 3.2 3.2

    It bounces around a bit, but it actually gets worse for the large units.

    I do note that my Koi - up to 18" - were just fine with up to 6" of ice on the pond. (the pond was 1.5m deep)
    (a bubbler under the ice is _important_, or they will die.)
  • Roger Thanks for the reply. So to chose a unit for a heating supplement to heat in summer it would be the 50Hs-A But for the winter you could get away with the smaller one 35Hs-A. However the smaller one is probably not enough heat and would be running continously
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.