Running electric cables under radiator pipes

Hi all,
My builder moved radiator pipes underneath the concrete floor in the living room, and then also moved electric cables in that room under the floor. As you can see from the photos, in two places, the cables (which are in trunking) and pipes cross each other.

http://imageshack.us/photo/my-images/849/phototqu.jpg/
http://imageshack.us/photo/my-images/823/photo2tu.jpg/

I wondered how safe this configuration was. Could it pass Part P?Do I need to ask the builder to find another way of sending cables around the living room?

thanks to all that reply!

Comments

  • greyteam1959
    greyteam1959 Posts: 4,752 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Looks a right bodge job to me................
  • sirhobo
    sirhobo Posts: 56 Forumite
    In situations like these, where you need to get electrics to the other side of the room, what should the builder be doing? Running the cables behind walls and around door frames?
  • cyclonebri1
    cyclonebri1 Posts: 12,827 Forumite
    What temp do you think the water pipe gets up to??.

    60 degrees max and possibly 100 under energency conditions.

    The only issue you have there is if the cable/pipes are actually touching, but the insulation will not melt at that temp, + the cables are in conduit that insures there is an air gap. The temp of the cable depends on the load in the circuit that short crossover will have no effect.
    I like the thanks button, but ,please, an I agree button.

    Will the grammar and spelling police respect I do make grammatical errors, and have carp spelling, no need to remind me.;)

    Always expect the unexpected:eek:and then you won't be dissapointed
  • sirhobo
    sirhobo Posts: 56 Forumite
    What temp do you think the water pipe gets up to??.

    60 degrees max and possibly 100 under energency conditions.

    The only issue you have there is if the cable/pipes are actually touching, but the insulation will not melt at that temp, + the cables are in conduit that insures there is an air gap. The temp of the cable depends on the load in the circuit that short crossover will have no effect.

    I agree having the insulation is somewhat reassuring.
  • mervyn11 wrote: »
    Looks a right bodge job to me................

    Why?

    Looks fine to me.
  • sirhobo
    sirhobo Posts: 56 Forumite
    Ok, so doesn't look like this job is a major disaster.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.5K Banking & Borrowing
  • 253.7K Reduce Debt & Boost Income
  • 454.5K Spending & Discounts
  • 245.5K Work, Benefits & Business
  • 601.5K Mortgages, Homes & Bills
  • 177.6K Life & Family
  • 259.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.