Boiler banging and pressure fluctuation

I have a Potterton Promax combi HE Plus, which is about Three years old.
The central heating appears to be fine, however when I run the hot water I get a a horrible knocking/banging sound from inside the boiler and the pressure fluctuates between 1 and 1.5 bar, the noise stops as soon as the hot water tap/shower is turned off and the pressure immediately stabilises. This does not happen all the time I would say about 1/3.
My questions:
Is this likely to be an air lock, if so how can I remove it from the system?
Could my pump be at fault, should I call an engineer?





Please see clip below showing issue:

Comments

  • gas4you
    gas4you Posts: 2,602 Forumite
    The boiler is overheating due to lack of flow for some reason or another.

    First thought would be the pump, but you say the heating is working?

    I can think the other possibility would be the plate HE blocked if the rads are actually working properly
  • nickem
    nickem Posts: 54 Forumite
    Thanks for the quick reply - Is this dangerous?
    If it is the plate can this be cleaned or does it have to be replaced?
    Also is this something that has to be done by a heating engineer, any idea on the expected cost of part and replacement?
    Kind Regards,
  • gas4you
    gas4you Posts: 2,602 Forumite
    Depending on the problem, the plate could be chemically cleaned, but as Potterton parts are some of the most reasonably priced around, it could be better to replace, but you would need someone in front of the boiler to confirm the fault before spending any sum of money.

    Are you 100% certain the pump is working properly?
  • nickem
    nickem Posts: 54 Forumite
    I appreciate your comments on this matter, you have been a great help. Is there a surefire way of knowing if the pump is working correctly, It would be nice to eliminate it?

    Kind Regards
  • garethgas
    garethgas Posts: 2,477 Forumite
    Proving the pump is ok isn't as straightforward as it might seem. There are lots of other noises going on so it can be tricky unless you can remove the centre screw and see the shaft spinning.
    Also, it might be intermittent so although you check and confirm its working, it might still be the cause.
    I'm suprised though that your not getting any error codes showing up.
    You have been reading.....another magnificent post by garethgas :beer:
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.8K Work, Benefits & Business
  • 619.5K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.