Earth cable sparking

I have just fitted an earth terminal block in order to bond a new tv aerial amplifier. To fit the block I simply cut into one of the earth cables from the main earthing point (PME) and rejoined it through the earth block. All well and good so far.

However as I rejoined the earth cable on the consumer unit side there was a slight spark. Not the full blown short of mains, more like the spark when you reconnect a car battery. I was able to repeat the spark just to make sure I hadn't imagined it.

The consumer unit in question has a 30mA Rcd covering most of the circuits, and I don't have any other faults.

Can anyone tell me what is causing this?

Thanks in advance
if i had known then what i know now

Comments

  • YorkshireBoy
    YorkshireBoy Posts: 31,541 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    cash99 wrote:
    ...I simply cut into one of the earth cables from the main earthing point (PME) and rejoined it through the earth block. All well and good so far.

    I like the use of the phrase "simply cut into the earth cables". The next time we see it, it will look something like...

    Here lies CASH99 - he "simply cut into the earth cables" - RIP

    The wire you "simply cut into" would/should have had a label attached at it's termination point(s) stating "SAFETY ELECTRICAL CONNECTION - DO NOT REMOVE".

    Playing with main earthing conductors is extremely dangerous on PME systems (in fact on any electrical system). This kind of work should be left to the professionals.

    By the way, the technical answer to your question is circulating neutral/earth currents resulting from increased potential difference - it would take much longer to put it into laymans terms. Lets leave it there.

    Finally, did you really need "protective earthing" which is sort of what you've done, or was it only "functional earthing" (as in BT systems) that was required?

    Take care and STAY SAFE.

    YB
  • cash99
    cash99 Posts: 274 Forumite
    Part of the Furniture 100 Posts Combo Breaker
    By the way, the technical answer to your question is circulating neutral/earth currents resulting from increased potential difference - it would take much longer to put it into laymans terms. Lets leave it there.


    Yorkshire Boy - So this is normal, and not a fault then?
    I like the use of the phrase "simply cut into the earth cables". The next time we see it, it will look something like...

    Here lies CASH99 - he "simply cut into the earth cables" - RIP

    Believe me I have a very healthy regard for electrical safety.I have seen the effects of elctrocution first hand when the electricity board came to move my supply. One electrician had to be resuscitated and his mate nearly joined him when he tried to garb hold of him.

    The wire you "simply cut into" would/should have had a label attached at it's termination point(s) stating "SAFETY ELECTRICAL CONNECTION - DO NOT REMOVE".


    It didn't but it does now, and the cable has not been removed.

    Finally, did you really need "protective earthing" which is sort of what you've done, or was it only "functional earthing" (as in BT systems) that was required?

    I have fitted a loftbox tv aerial amplfier which has a separate earth stud which the intructions say should be earth bonded back to the main electrical earth bonding. I believe this is to do with lightning hitting the tv aerial. Presumably this is correct otherwise the coax cable conected to the amplifier would become live if the aerial is hit by lightning.

    Thanks for the reply
    if i had known then what i know now
  • Pink.
    Pink. Posts: 17,652 Forumite
    10,000 Posts Combo Breaker
    Just a reminder of the warning at the top of this board:

    Pink
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.9K Banking & Borrowing
  • 252.7K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.8K Work, Benefits & Business
  • 619.7K Mortgages, Homes & Bills
  • 176.4K Life & Family
  • 255.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.