PLEASE READ BEFORE POSTING: Hello Forumites! In order to help keep the Forum a useful, safe and friendly place for our users, discussions around non-MoneySaving matters are not permitted per the Forum rules. While we understand that mentioning house prices may sometimes be relevant to a user's specific MoneySaving situation, we ask that you please avoid veering into broad, general debates about the market, the economy and politics, as these can unfortunately lead to abusive or hateful behaviour. Threads that are found to have derailed into wider discussions may be removed. Users who repeatedly disregard this may have their Forum account banned. Please also avoid posting personally identifiable information, including links to your own online property listing which may reveal your address. Thank you for your understanding.
We're aware that some users are experiencing technical issues which the team are working to resolve. See the Community Noticeboard for more info. Thank you for your patience.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
MCB needs replacing on house circuits to sell or not?
Options
Comments
-
Regardless of what code a Periodic inspection and test brings up, it will highlight anything non compliant with the current regulations therefore when selling the house showing the results to any prospective buyer will show what needs doing without any comeback on the OP.
As for wiring a house is easy, please I hope you said that in jest as electrics is far from a simple job.
No jest involved, if you do your homework domestic electrics in a typical house are simple, what do you think is so complicated about them? As with all things if someone is not comfortable with doing them then they shouldn't but for a lot of competant DIYers a rewire is within their scope but of course now Part P is in force they can't (shouldn't) do this.I have a lot of problems with my neighbours, they hammer and bang on the walls sometimes until 2 or 3 in the morning - some nights I can hardly hear myself drilling0 -
Homersimpson wrote: »No jest involved, if you do your homework domestic electrics in a typical house are simple, what do you think is so complicated about them? As with all things if someone is not comfortable with doing them then they shouldn't but for a lot of competant DIYers a rewire is within their scope but of course now Part P is in force they can't (shouldn't) do this.
Please don't say something like this.
There are several things that make this a not so simple job, such as volt drop, cable calculations, what type of earth set up for maximum zs permitable. Just to mention a few things that aren't what they seem to the naked eye.
Oh and as for part P, you can get your local authority to certify it for a fee, so saying you cant or shouldn't do it because of this is wrong too.0 -
Homersimpson wrote: »No jest involved, if you do your homework domestic electrics in a typical house are simple, what do you think is so complicated about them? As with all things if someone is not comfortable with doing them then they shouldn't but for a lot of competant DIYers a rewire is within their scope but of course now Part P is in force they can't (shouldn't) do this.
I have to agree. I would never attempt it myself, but would support anyone who was willing to read up/learn and then DIY if they felt confident enough. Same with servicing my car.
I regularly have this same debate here about DIY conveyancing, which I have done. It's all about recognising ones own skills, capabilities and limitations.0 -
Please don't say something like this.
There are several things that make this a not so simple job, such as volt drop, cable calculations, what type of earth set up for maximum zs permitable. Just to mention a few things that aren't what they seem to the naked eye.
Oh and as for part P, you can get your local authority to certify it for a fee, so saying you cant or shouldn't do it because of this is wrong too.
If you have a read of the IEE on-site guide it explains in simple terms how to wire a small installation such as a house. It even gives rules of thumb for cable sizes for areas covered.
As for maximum Zs, did you know that Zs is almost irrelevant in a house with 30mA RCD's on all circuits, if your Zs is less than around 1666 ohms it will comply (Zs of a ringmain circuit wouldn't usually exceed 1 ohm depending upon Ze) Stop trying to make it sound complicated it really isn't go someone who is prepared to do some reading.I have a lot of problems with my neighbours, they hammer and bang on the walls sometimes until 2 or 3 in the morning - some nights I can hardly hear myself drilling0 -
I am not making it sound complicated, you are the one saying go for it. Its easy.
All I am doing is pointing whats needs to be correct before carrying out the work. yes I know what a maximum Zs value is, besides it is almost irrelevant isnt an excuse because it can be that high doesn't distinguish from the fact it still has to comply within a certain criteria.
If its that simple simple what about K values which surely are safely critical?0 -
"If its that simple simple what about K values which surely are safely critical?"
Do you mean K factor for working out the thermal constraint of cables i.e K2S2 and then comparing to the I2t of the protective device? or a K rating of transformer for inrush and harmonic distortion?
In my years of experience of designing electrical systems its rare to have a problem with K2S2 except on the fire alarm panel to a large building because the cable size is very small for its point of connection to the system, i.e its connected to the main switch panel fed by a 1000kVA transformer with a prospective short circuit current (PSCC) of around 32kA.
I've never seen a domestic property with a PSCC which would cause a problem for T+E, even when right next to the substation, the resistance of the main and service cables brings it down to a low enough level. If I had a copy of my regs book I could work out what the PSCC would have to be to cause a problem for a 32A ring, it would be huge.
I'm bored arguing with you now as you clearly know it all, I take it all back everyone electrity - be afraid be very afraid.I have a lot of problems with my neighbours, they hammer and bang on the walls sometimes until 2 or 3 in the morning - some nights I can hardly hear myself drilling0 -
Well, Homer, you maybe bored of arguing, I however would like to thank you and a number of others on this thread already for your advice and level of practicallity and common sense applied in my situation. I do agree regarding letting my solicitor doing my electrical work, however I also think that neither should my electrician to make me pay for fillings that I may not need.
At the end of the day, I am a compentent DIY'er with a very good understanding of how to wire a house and the time and patience to read up on how to do it. I was happy to get someone out to check and sign off my work as part of the regulations and it was all in an exposed and accessable in order that had I over looked something, then it would easily be rectifiable in order to pass. It is right that not everyone has the mentality or skill to do that and the biggest problem are those whom do not know their limitations, not those that do and are confident in what they do.
To be perfectly honest, I am going to do exactly the same at my new house, it is an old house with old box so would fail in exactly the same way as I have just fallen over this time. It is not going to stop me doing a certain amount of rewiring when I get around to it (the kitchen springs to mind) also know my limitations and am "not afraid to ask my local sparky" if I need, yes it involves a call out charge sometimes, but it's still cheaper than blundering on and hoping I got it right when he comes to check at the end. Also it makes it cheaper and more importantly safer in the long run.
It also annoys me that I have to get my gas checked. I have replumbed my old house top to toe (water lead pipes) and never had a leak, I don't see why my cooker had to be checked, yet that not. Anyway, separate arguement, as I could argue the other side if I wanted to.
Thanks for the help is really all I wanted to say here, you made me rant a little reading the rest of the thread hahaha0 -
... At the end of the day, I am a compentent DIY'er with a very good understanding of how to wire a house and the time and patience to read up on how to do it. I was happy to get someone out to check and sign off my work as part of the regulations and it was all in an exposed and accessable in order that had I over looked something, then it would easily be rectifiable in order to pass. It is right that not everyone has the mentality or skill to do that and the biggest problem are those whom do not know their limitations, not those that do and are confident in what they do.
To be perfectly honest, I am going to do exactly the same at my new house, it is an old house with old box so would fail in exactly the same way as I have just fallen over this time. It is not going to stop me doing a certain amount of rewiring when I get around to it (the kitchen springs to mind) also know my limitations and am "not afraid to ask my local sparky" if I need, yes it involves a call out charge sometimes, but it's still cheaper than blundering on and hoping I got it right when he comes to check at the end. Also it makes it cheaper and more importantly safer in the long run.
It also annoys me that I have to get my gas checked. I have replumbed my old house top to toe (water lead pipes) and never had a leak, I don't see why my cooker had to be checked, yet that not. Anyway, separate arguement, as I could argue the other side if I wanted to.
Thanks for the help is really all I wanted to say here, you made me rant a little reading the rest of the thread hahaha
I also want to add an RCD in the feed to the fusebox. This is undoubtedly safer and my only way of providing RCD protection to the whole house in the short to medium term - because I know that it won't be possible to replace the current fusebox with a split load unit without reworking most of the first runs.
If I do add the RCD, then I will be non compliant with 314.1 iv. Someone could bump their head turning the lights back on after the RCD has tripped [having survived electrocution because the RCD did trip]. It is obvious that the right course is to effect some improvement, but the non compliance will give me exactly the same problems you are having on selling the property.Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.8K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.8K Work, Benefits & Business
- 598.7K Mortgages, Homes & Bills
- 176.8K Life & Family
- 257.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards