Remeha Avanta 24S System Boiler Leaking

droid1978
Posts: 60 Forumite
I have a Remeha Avanta 24S System Boiler which is two years old. I have noticed that it is making a popping noise and there was small leak. Last night I topped it beyond 1 bar, this evening now it is below 1 bar.
However, it is still functioning and no error code has been displayed.
Please can someone help me.
However, it is still functioning and no error code has been displayed.
Please can someone help me.
Smile and be happy, things can usually get worse!
0
Comments
-
You need to find where the leak is.
As it is 2 years old, it will not have been fitted with a low pressure sensor that will stop the boiler firing if the system pressure drops.
This is only a fairly recent addition to these boilers and as such will not give a fault code when the pressure drops on new ones. It will just sit there not working.
When was your boiler last serviced and set up?0 -
I have topped it up and it lost pressure overnight. The pressure is underneath a bar. The boiler is still working though.
It is coming from underneath boiler as put some newspaper underneath it. It is not a consistent flow. Could it be the valve underneath it? Should I not be using it?
It was installed in August 2009. I have not had serviced since then.Smile and be happy, things can usually get worse!0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 349.9K Banking & Borrowing
- 252.7K Reduce Debt & Boost Income
- 453K Spending & Discounts
- 242.9K Work, Benefits & Business
- 619.7K Mortgages, Homes & Bills
- 176.4K Life & Family
- 255.8K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 15.1K Coronavirus Support Boards