We’d like to remind Forumites to please avoid political debate on the Forum.

This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.

The MSE Forum Team would like to wish you all a Merry Christmas. However, we know this time of year can be difficult for some. If you're struggling during the festive period, here's a list of organisations that might be able to help
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
Has MSE helped you to save or reclaim money this year? Share your 2025 MoneySaving success stories!

I've wired electric fire into wall switch...help on fuse size please

I wired in my electric fire under the floor boards and to a wall socket and then turned it on. It cut out after maybe 20mins.
There was a 13amp fuse in the switch. I had just cut off the original plug and stripped it back.

Before replacing it, I'd like to check is this likely to be sufficient fuse size and/or reason for cut out.
I have it wired in correctly to one of those white switches with a red light. Thanks

Comments

  • ormus
    ormus Posts: 42,714 Forumite
    13 amp is the max size to use. has the fire got a thermal cut out safety device?
    otherwise the fire maybe faulty. beware.
    Get some gorm.
  • Hi,
    edtheduck wrote: »
    I have it wired in correctly to one of those white switches with a red light.

    was that maybe originally used for a storage heater, if so you will be on a timed circuit, so fire will only operate at preset times.

    Do you or did you have electric storage heating?
  • You say you ran it under the floorboards, when you put the boards back down was there any chance of them compressing the cable? This could be the reason for it running for 20mins then cutting out, so it could be a compression fault

    Secondly the circuit you connected too is this a circuit of its own or part of the ring, if on its own then check the size of the circuit breaker back at the fuse board and see if any breakers are down.

    Thirdly put the fuse in and see if the red light comes back on this will let you know that everything is ok at the board and the breaker has not tripped.

    Lastley, it could be a loose connection when you connected it up.

    There are other faults it could be but those are most commen.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.9K Banking & Borrowing
  • 253.9K Reduce Debt & Boost Income
  • 454.7K Spending & Discounts
  • 246K Work, Benefits & Business
  • 602.1K Mortgages, Homes & Bills
  • 177.8K Life & Family
  • 259.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.