Combi boiler water pressure dropping

Our ferroli combi boiler needs re pressurising every day as it drops to almost nothing. What's likely to be the cause and would it be an easy job to fix? Will be getting a service on it asap.

Comments

  • ariba10
    ariba10 Posts: 5,432 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    You must be loosing water somewhere,

    Either a small leak or you are setting the pressure too high when you fill it, and the excess water is being vented, as the system heats up.
    I used to be indecisive but now I am not sure.
  • keystone
    keystone Posts: 10,916 Forumite
    Pressure when cold should be iro 1 bar.

    Pressure when hot should be iro 2 bar.

    If when hot pressure rises to iro 3 bar the PRV will lift to relieve the pressure.

    If they have lifted inevitably carp gets in the seating and it doesn't reseat properly and then it starts passing.

    So check the PRV drain to see if its wet or dripping. If so get PRV checked.

    If not get the expansion vessel checked as it either needs recharging or the diaphragm is knackered.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • when cold and we re pressurise it we let it get to 1 and thats it. we then put ther heating on for a few hours and by the next day its back down to zero. Will look into what youve suggested thanks, and get it serviced too!
  • gas4you
    gas4you Posts: 2,602 Forumite
    Sounds like the expansion vessel either needs re-pressurising, or is knackered and needs replacing.

    If you can find the car type valve on it, press the pin. If water comes out it is knackered, if nothing (no air or water) it needs re-pressurising, which will (should) be included in the service.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.2K Banking & Borrowing
  • 253.6K Reduce Debt & Boost Income
  • 454.3K Spending & Discounts
  • 245.3K Work, Benefits & Business
  • 601K Mortgages, Homes & Bills
  • 177.5K Life & Family
  • 259.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.