electtic shock - RCB did not trip

2

Comments

  • hardpressed
    hardpressed Posts: 2,099 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    The moral of this story is never, ever leave a lamp without a light bulb. It's just an accident waiting to happen.
  • vaio
    vaio Posts: 12,287 Forumite
    Part of the Furniture 10,000 Posts Combo Breaker
    Nah, the moral is don't stick your fingers into empty bulb holders, especially if they are on
  • keystone wrote: »
    In the limit you are absolutely correct, of course, which is why:

    1. With older non-double insulated metal light fittings a tingling sensation can sometimes be felt when touching it and;

    2. Even with an MCB in the off position (MCBs being usually single pole) the circuit it protects is never truly dead and your meter can register a very small current t'wixt neutral and earth.

    However, IIRC the pd between neutral and earth needs to be of the order of 50 volts to generate the 34mA current sufficient to trip an RCD so a very small pd of the order of 1 or 2 volts will not cause the RCD to trip.

    Cheers

    when ever i put neutral to earth .My rcd trips
    SO either DVardysShadow is right or my system has something wrong.

    all the best.markj
  • keystone
    keystone Posts: 10,916 Forumite
    edited 26 October 2010 at 9:11AM
    when ever i put neutral to earth .My rcd trips
    SO either DVardysShadow is right or my system has something wrong.

    all the best.markj
    No you cannot draw that conclusion from the post you quoted - read it again.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • vaio
    vaio Posts: 12,287 Forumite
    Part of the Furniture 10,000 Posts Combo Breaker
    keystone wrote: »
    In the limit you are absolutely correct, of course, which is why:

    1. With older non-double insulated metal light fittings a tingling sensation can sometimes be felt when touching it and;

    2. Even with an MCB in the off position (MCBs being usually single pole) the circuit it protects is never truly dead and your meter can register a very small current t'wixt neutral and earth.

    However, IIRC the pd between neutral and earth needs to be of the order of 50 volts to generate the 34mA current sufficient to trip an RCD so a very small pd of the order of 1 or 2 volts will not cause the RCD to trip.

    Cheers

    Nah, the 50V figure is the voltage general held to be sufficient to cause a noticeable shock to a human. Ie Enough to drive current through the impedance of a human body. (couple of thousand ohms)

    RCD’s trip with shorted N-E with only a volt or two on the N because the impedance is much lower
  • missile
    missile Posts: 11,779 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    Change out that nurse (and the bulb) for a newer, younger, more energy efficient model.
    "A nation's greatness is measured by how it treats its weakest members." ~ Mahatma Gandhi
    Ride hard or stay home :iloveyou:
  • 27col
    27col Posts: 6,554 Forumite
    Or you could buy one of those IKEA/ Wilkinson's/BHS bedside lamps that you just tap with your fingers to make them come on or off. No need then to put your fingers anywhere near the lamp holder.
    I can afford anything that I want.
    Just so long as I don't want much.
  • DVardysShadow
    DVardysShadow Posts: 18,949 Forumite
    keystone wrote: »
    However, IIRC the pd between neutral and earth needs to be of the order of 50 volts to generate the 34mA current sufficient to trip an RCD so a very small pd of the order of 1 or 2 volts will not cause the RCD to trip.
    1 volt will give 34mA with a neutral earth loop impedance of 294 Ohms. For 50V, the neutral earth loop impedance would be 14705 Ohms. If the value were above 10 Ohms, that would be an rather poor neutral earth loop impedance. A fraction of a voltbetween neitral and earth will be sufficient to trip an RCD
    vaio wrote: »
    Nah, the 50V figure is the voltage general held to be sufficient to cause a noticeable shock to a human. Ie Enough to drive current through the impedance of a human body. (couple of thousand ohms)

    RCD’s trip with shorted N-E with only a volt or two on the N because the impedance is much lower
    I agree with this. Perhaps there is some confusion withe the old style Voltage Operated Earth Trip switch? These were designed to ensure that the potential of bonded metal did not rise more than 40V above earth potential IIRC. These were designed to be used in situations with horrendously high earth loop impedances.
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam
  • keystone
    keystone Posts: 10,916 Forumite
    vaio wrote: »
    Nah, the 50V figure is the voltage general held to be sufficient to cause a noticeable shock to a human. Ie Enough to drive current through the impedance of a human body. (couple of thousand ohms)
    Ta. I obviously didn't recollect correctly. Must be getting old. :D

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • keystone
    keystone Posts: 10,916 Forumite
    Perhaps there is some confusion withe the old style Voltage Operated Earth Trip switch?
    Yes you could well be onto something there - I was dragging stuff out of the memory banks after all.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.5K Banking & Borrowing
  • 253.3K Reduce Debt & Boost Income
  • 453.9K Spending & Discounts
  • 244.5K Work, Benefits & Business
  • 599.8K Mortgages, Homes & Bills
  • 177.2K Life & Family
  • 258.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.