Combi Problems

Options
Hello everybody, first post. I have a 6 year old potterton 80 combi that is playing up, if you run a bath or take a shower the boiler will lock out. If you turn on the washer there is a noise like a motorbike starting up from the pipes, and sometimes the heating is coming on with the hot water and you have to turn on the cold tap to stop it. The boiler is insured and has had 3 pumps and a circuit board in 6 years. I had the boiler serviced last week and the guy said it could need a powerflush, i ran off some water from one of the radiators and it is crystal clear.The radiators are also piping hot all over.When the pumps have been replaced (one lasted 3 weeks) there has not been a lot of sludge built up in them. I have not claimed on the insurance as it is still working (after a fashion) and i was told by the service engineer if its sludge i am not covered. any ideas please??
Cheers

Comments

  • How old is the radiators and the rest of the system?
  • alanobrien
    alanobrien Posts: 3,308 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker Mortgage-free Glee!
    stevegray wrote:
    sometimes the heating is coming on with the hot water and you have to turn on the cold tap to stop it.
    Cheers

    Sounds like a dodgy diverter valve to me, if i were you i would be getting another corgi engineer in to look at it.
  • MarkyMarkD
    MarkyMarkD Posts: 9,912 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    It sounds like whoever has been repairing it doesn't have a clue about the fault - 3 pumps, for goodness's sake!

    I would definitely support alanobrien's view - and if a sensible engineer diagnoses the actual fault, claim off the useless insurance people.
  • Skiduck
    Skiduck Posts: 1,973 Forumite
    I'd support Alan's view aswell - sounds like the "paddle" on the valve is knackered. You do not need a powerflush as the whole of the radiator is hot, don't let him con you into one.
    However the lock out could be another problem, possivbly a flow switch - also are there any dripping taps?
  • Thanks for the replys, there are no leaking taps and the lockout happens when the hot water has been running constantly for a few minutes. Wolud the diverter valve cause the noisy pipes, heating coming on etc?
    Thanks again
  • Skiduck
    Skiduck Posts: 1,973 Forumite
    stevegray wrote:
    Thanks for the replys, there are no leaking taps and the lockout happens when the hot water has been running constantly for a few minutes. Wolud the diverter valve cause the noisy pipes, heating coming on etc?
    Thanks again


    The diverters acts basically as a rudder, directing the hot water from the boiler to either the CH system or the DHW. If this was faulty there may be a chance that the rudder is not being held in any position (either to shut out the CH flow or the DHW flow) thus just "flapping around" willy and indeed nilly. There will be some tension in the "rudder" when the diverter is changing, but this will still make the rudder kind of "clap" - hence noise in the radiator circuit and strange goingson in the DHW.

    I would say that the diverter is failing on the DHW side
  • Andybez38
    Andybez38 Posts: 1,773 Forumite
    Part of the Furniture Combo Breaker
    Skiduck wrote:
    The diverters acts basically as a rudder, directing the hot water from the boiler to either the CH system or the DHW. If this was faulty there may be a chance that the rudder is not being held in any position (either to shut out the CH flow or the DHW flow) thus just "flapping around" willy and indeed nilly. There will be some tension in the "rudder" when the diverter is changing, but this will still make the rudder kind of "clap" - hence noise in the radiator circuit and strange goingson in the DHW.

    I would say that the diverter is failing on the DHW side

    I think Skiduck is right ;)
    I came into this world with nothing and I'm gonna leave with nothing.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.