power shower question - electric supply?

Options
Hi,

long old story but I initially bought a Mira Platinum shower suitable for low pressure gravity fed systems - which I have. Decided not to have that one fitted so took it back. Bought instead a Mira Vigour also for low pressure systems.

When Sparky was here, I had him put a spur in loft above where shower will be (this was when i was having the Platinum)

fast forward to now, bathroom all fitted except the Vigour. fitter said that it was to do with the electric supply? said he ddn't want to fry himself when fitting!

I took it back to the plumbers merchants. a plumber happened to be in there and said it just needs a 13 I think he said - might have been 15, socket. I can't see what the problem is with it.

any ideas please?
Mortgage free as of 10/02/2015. Every brick and blade of grass belongs to meeeee. :j

Comments

  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    The installation instructions make it quite clear what is required, you can't just use any old socket. What circuit has the spur been taken off?


    Electrical
    Power supply - 230-240 V at 50 Hz, fused at 3 Amps, via a double pole fused switch (not supplied) with a minimum contact separation of 3 mm for each contact.

    Electrical Connections - Terminal block will accept cable up to 2.5 mm². Minimum cable size (cross-sectional area) required under normal installation conditions is 1 mm2.
    Power Consumption - 150 W maximum.
    No free lunch, and no free laptop ;)
  • spirit
    spirit Posts: 2,886 Forumite
    Part of the Furniture Combo Breaker Mortgage-free Glee!
    thanks macman, sparky is popping round this evening to look. i suspect the fitter fobbed me off a bit. i texted him to ask what was the problem as the plumbers merchants were a bit baffled by his reasoning.

    i've had a text back from fitter to say "i will call in there later and have a chat with them and try to sort it"

    i assume he means with City Plumbing.

    most odd
    Mortgage free as of 10/02/2015. Every brick and blade of grass belongs to meeeee. :j
  • KeithP
    KeithP Posts: 41,296 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Spirit, what was the outcome?
  • spirit
    spirit Posts: 2,886 Forumite
    Part of the Furniture Combo Breaker Mortgage-free Glee!
    Hello Keith,

    it's been something of a nightmare. However having spoken to the fitter again and my sparky, it would seem that the fitter thought the power shower was an electric one as in heats the water as you use it. Sparky said that this type does need the thicker cable and wiring back to the fuse board. However the one I bought was not of this type and just runs off a 5 amp socket. By this time I'd already taken the shower back on fitters advice. To be fair to the fitter, he does not claim to know a lot about electrics and has made a good job of the bathroom so far.

    So, back to square 1. The plumbers merchant recommended the first shower I bought :eek:
    Mortgage free as of 10/02/2015. Every brick and blade of grass belongs to meeeee. :j
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.