Electrical quote (to get Part P)

Options
scrimmager
scrimmager Posts: 2 Newbie
edited 9 May 2010 at 7:49PM in Is this quote fair?
Hi,

Trying to get a part P (sparks uncontactable after doing the work and gfriend discovered she needed Part P!) so had an inspection done and what follows is the problems identified and quoted to fix for £1000 + Vat. Recommended dual RCD consumer unit. House is a Victorian 2 bed terrace, with electrics pretty modern (ie. 10yr old C Unit)

1. Out building fed from kitchen sockets circuit, circuit overloaded,remove c\u in out building (out building is outside toilet attached to kitchen)

2. Circuit 7 not identified on board

3. Cables in corner of cellar through crimped and left exsposed

4. Spur for intruder alarm not identified

5. 6 Bathroom spots not fire rated,4 spot lights on landing,connected in roof space with choc block connectors

6. No equipotential bond to gas

7. Main earth undersized

General condition good
requires some improvements to bring it inline with regs

Remove mcbs from out building and incorporate sockets into kitchen ring
Replace spots with fire rated spots and connectors

Cable sticking out of corner of out building
Cables sticking out of wall in kitchen
No warning labels or test stickers
No equipotential bond to Gas
«1

Comments

  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    Hi, Where abouts are you in the country?
  • Midlands, cheers
  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    edited 9 May 2010 at 8:58PM
    scrimmager wrote: »
    Hi,

    Trying to get a part P (sparks uncontactable after doing the work and gfriend discovered she needed Part P!)

    What work has your sparks already done?
    scrimmager wrote: »
    so had an inspection done and what follows is the problems identified and quoted to fix for £1000 + Vat.

    Who did the inspection?
    scrimmager wrote: »
    Recommended dual RCD consumer unit. House is a Victorian 2 bed terrace, with electrics pretty modern (ie. 10yr old C Unit)

    Does the existing CCU (Consumer Unit) have an RCD? What reasons were identified which required a new CCU?
    scrimmager wrote: »
    1. Out building fed from kitchen sockets circuit, circuit overloaded,remove c\u in out building (out building is outside toilet attached to kitchen)
    What is overloading the circuit?
    So are you saying that the CCU for the house is in the outbuilding?
    scrimmager wrote: »
    2. Circuit 7 not identified on board
    3. Cables in corner of cellar through crimped and left exsposed
    4. Spur for intruder alarm not identified
    5. 6 Bathroom spots not fire rated,4 spot lights on landing,connected in roof space with choc block connectors
    scrimmager wrote: »
    6. No equipotential bond to gas
    Where is the Gas meter in relation to the CCU?
    scrimmager wrote: »
    7. Main earth undersized
    This is dependent upon the main cut-out fuse...Do you know what the main supply fuse rating is. (It should be identified on your PIR.) Also, what is the current size of the main earth, and what are the earthing arrangements of the supply. (I.e. TNCS(PME), TNS, TT)
    scrimmager wrote: »
    General condition good
    requires some improvements to bring it inline with regs

    On the report, was the property given a 'Satisfactory' or 'Unsatisfactory'
    scrimmager wrote: »
    Remove mcbs from out building and incorporate sockets into kitchen ring
    I am a bit confused on the above...are you saying that there is a small consumer unit with MCBs in the outbuilding, which is the overloaded circuit? Can you please clarify.
    scrimmager wrote: »
    Replace spots with fire rated spots and connectors
    Or you can just add fire-hoods to the spots.

    scrimmager wrote: »
    Cable sticking out of corner of out building
    Cables sticking out of wall in kitchen
    No warning labels or test stickers
    No equipotential bond to Gas
    Ok

    Additionally, All items highlighted in the report should have been given a code 1 to 4...do you have this detail
  • zax47
    zax47 Posts: 1,263 Forumite
    Yooj, it's a CU - Consumer Unit, not a CCU. Small thing I know, but as a sparky it's irritating me, sorry.
  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    zax47 wrote: »
    Yooj, it's a CU - Consumer Unit, not a CCU. Small thing I know, but as a sparky it's irritating me, sorry.

    I think you'll find it is a Consumer Control Unit, just shortened to Consumer Unit
  • baldelectrician
    baldelectrician Posts: 2,467 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Yooj wrote: »
    I think you'll find it is a Consumer Control Unit, just shortened to Consumer Unit

    It's a consumer unit , a CCU is a COOKER CONTROL UNIT (usually meaning a cooker switch with an integrated socket)

    Cooker control unit;

    MKK5001.JPG
    baldly going on...
  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    edited 9 May 2010 at 10:14PM
    I suggest you check the regs then.

    Though this is not really answering the OPs question is it.
  • zax47
    zax47 Posts: 1,263 Forumite
    edited 9 May 2010 at 10:39PM
    Thank B-E, nice to see you over here again. Keep spotting you in several other sparky forums too.
  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    "Consumer Unit also known as a Consumer Control Unit" Reference - Part 2 Definitions in the Big Red Book...I prefer that, than the Ultimate Handyman...

    As to saying that whether CCU is not refered to as a Consumer Unit...maybe you should go and search for posts relating to CCU on the IET website and see how many responses you get back regarding Cooker Control Units.

    Though like I said, this is not really progressing the OPs question is it.

    Yooj
  • Yooj_2
    Yooj_2 Posts: 96 Forumite
    Page 22 - PART 2 definitions
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244K Work, Benefits & Business
  • 598.8K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.3K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.