Electric Cooker connection question.
uncle_buck_3
Posts: 360 Forumite
Hi,
When connecting a built in electric oven (5 kW) & ceramic hob (6.5 kW) what would be the recommended method of connection?
…..do the regs allow you to put both the cables into the single cooker connection point?
UB.
When connecting a built in electric oven (5 kW) & ceramic hob (6.5 kW) what would be the recommended method of connection?
…..do the regs allow you to put both the cables into the single cooker connection point?
UB.
0
Comments
-
no the regs dont allow it,and im not electrician but thers a max amount of volts you can have runnin through one line, you could go up in smoke! lol, we had our kitchen installed 4 weeks ago. cookers on a seprate main ringYou're not drunk if you can lie on the floor without holding on0
-
I think uncle_buck is just checking up that his NICEIC registered, Part-P qualified electrician is telling the truth.Al_Mac wrote:Don't they say it has to be fitted by a competent pro now?
0 -
Yes they do actually.robwend wrote:no the regs dont allow it,
I figured.and im not electrician
'Volts' are irrelevant.but thers a max amount of volts you can have runnin through one line,
Very trueyou could go up in smoke!
Cookers are installed on a single 'radial' circuit, not a 'ring'.cookers on a seprate main ring
The answer to the OP's question is...
Yes, both applicances can be connected to the one isolation/switching device.
However, other factors will come into play (cable sizing, application of diversity, selection of appropriate protective device, grouping, thermal insulating barriers, and length of cable run).
As Al Mac says, you need a professional.0 -
So you did.Al_Mac wrote:I said that;)
0 -
YorkshireBoy wrote:The answer to the OP's question is...
Yes, both applicances can be connected to the one isolation/switching device.
Thanks for that…. I wasn’t sure if the regs allowed you to connect like this.
Yeah I’ve done the diversity calculation….. (10 A + 30% balance + 5 A for socket)
Total load 11.5 kW….(No socket)
11500 / 240 = 47.91A (call it 48)
48A – 10A = 38A
38A / 30% = 11.4A
10A + 11.4A = 21.4A
The new cooker / hob will be fed from the existing cooker point that is fed in 6mm T&E with a 30A cartridge fuse.
….Yeah I am just checking that the NICEIC registered, Part-P qualified electrician that is doing the job isn’t cutting any corners
UB.0 -
i should remember never to type anything about electrics lmao!!!!!You're not drunk if you can lie on the floor without holding on0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 354.3K Banking & Borrowing
- 254.4K Reduce Debt & Boost Income
- 455.4K Spending & Discounts
- 247.2K Work, Benefits & Business
- 603.9K Mortgages, Homes & Bills
- 178.4K Life & Family
- 261.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards