When connecting a built in electric oven (5 kW) & ceramic hob (6.5 kW) what would be the recommended method of connection?
…..do the regs allow you to put both the cables into the single cooker connection point?

UB.

Comments

  • robwend
    robwend Posts: 2,919 Forumite
    no the regs dont allow it,and im not electrician but thers a max amount of volts you can have runnin through one line, you could go up in smoke! lol, we had our kitchen installed 4 weeks ago. cookers on a seprate main ring
    You're not drunk if you can lie on the floor without holding on
  • YorkshireBoy
    YorkshireBoy Posts: 31,541 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Al_Mac wrote:
    Don't they say it has to be fitted by a competent pro now?
    I think uncle_buck is just checking up that his NICEIC registered, Part-P qualified electrician is telling the truth. ;)
  • YorkshireBoy
    YorkshireBoy Posts: 31,541 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    robwend wrote:
    no the regs dont allow it,
    Yes they do actually.
    and im not electrician
    I figured.
    but thers a max amount of volts you can have runnin through one line,
    'Volts' are irrelevant.
    you could go up in smoke!
    Very true
    cookers on a seprate main ring
    Cookers are installed on a single 'radial' circuit, not a 'ring'.



    The answer to the OP's question is...

    Yes, both applicances can be connected to the one isolation/switching device.

    However, other factors will come into play (cable sizing, application of diversity, selection of appropriate protective device, grouping, thermal insulating barriers, and length of cable run).

    As Al Mac says, you need a professional.
  • YorkshireBoy
    YorkshireBoy Posts: 31,541 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Al_Mac wrote:
    I said that;)
    So you did. :)
  • The answer to the OP's question is...
    Yes, both applicances can be connected to the one isolation/switching device.

    Thanks for that…. I wasn’t sure if the regs allowed you to connect like this.



    Yeah I’ve done the diversity calculation….. (10 A + 30% balance + 5 A for socket)

    Total load 11.5 kW….(No socket)

    11500 / 240 = 47.91A (call it 48)

    48A – 10A = 38A

    38A / 30% = 11.4A

    10A + 11.4A = 21.4A

    The new cooker / hob will be fed from the existing cooker point that is fed in 6mm T&E with a 30A cartridge fuse.


    ….Yeah I am just checking that the NICEIC registered, Part-P qualified electrician that is doing the job isn’t cutting any corners ;)


    UB.
  • robwend
    robwend Posts: 2,919 Forumite
    i should remember never to type anything about electrics lmao!!!!!
    You're not drunk if you can lie on the floor without holding on
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.3K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.2K Work, Benefits & Business
  • 603.9K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.