combi boiler/refilling

Hi I was wondering if anyone could help

I have a combi boiler about 3 years old

it seems to need topping up with water more than it used to, does anyone know why this would be?

thanks in advance
2007 £1749
2008 £291.99
2009 JanMasscara £7.00 Feb megcabot books x 2 £20 XFactor tkts x 2 £58.00 (couldn't go though as they only phoned on day :-( ) foundation £7.99
total so far for 09 £92.99
«1

Comments

  • Ionkontrol
    Ionkontrol Posts: 802 Forumite
    You have a leak somewhere.
    Go round every radiator and check all the valves to see if any are weeping.
  • dipsy
    dipsy Posts: 3,137 Forumite
    surely there would be a big water mark/evidence?

    I can't see anything obvious...... is there anything I can put into the boiler to seal wherever the leak is?
    2007 £1749
    2008 £291.99
    2009 JanMasscara £7.00 Feb megcabot books x 2 £20 XFactor tkts x 2 £58.00 (couldn't go though as they only phoned on day :-( ) foundation £7.99
    total so far for 09 £92.99
  • Hobsons_Choice
    Hobsons_Choice Posts: 1,123 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Ours was doing that, topped it up and now it leaks from the overflow pipe (outside).
    It may just be a faulty guage?
    Normal people worry me.
  • gas4you
    gas4you Posts: 2,602 Forumite
    Could be the prv leaking. Could be the expansion vessel needs re-pressurising or even replacing.

    When the heating is on, does the pressure rise very quickly to about 3 Bar?
  • dipsy
    dipsy Posts: 3,137 Forumite
    edited 7 April 2010 at 1:35AM
    ok checked it, and does this make any sense, If I leave the filler pipe the one that runs from tank to cold water source connected then there is less of an issue?.... but in answer to gas4, its the red dial, the one they set as suggested min level...it is set at 4 bar..., not sure if it reaches 3bar really quickly... what would that indicate?
    dont tell me knackered boiler as the guys I had come out left me withought heating/etc and the worcester/boch guy came out and said it was wired wrong.... and they came recomended....
    2007 £1749
    2008 £291.99
    2009 JanMasscara £7.00 Feb megcabot books x 2 £20 XFactor tkts x 2 £58.00 (couldn't go though as they only phoned on day :-( ) foundation £7.99
    total so far for 09 £92.99
  • macman
    macman Posts: 53,129 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Whether you leave the filling loop connected or not does not make any difference, as the valve on the loop is fully turned off (or should be) once it has been repressurised. Is it continually leaking from the pressure relief valve?
    It should not be reading 4 bar when cold!
    No free lunch, and no free laptop ;)
  • gas4you
    gas4you Posts: 2,602 Forumite
    The dial needle should read about 1.2 Bar when cold. Your prv is designed to open at 3 Bar, so at 4 bar you will have a constant leak.

    I would suggest you get this checked as well, because at 4 Bar it should be fully open and letting most of the pressure out.

    Check that your filling loop is properly closed and not passing water through.
  • ariba10
    ariba10 Posts: 5,432 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    gas4you wrote: »
    Could be the prv leaking. Could be the expansion vessel needs re-pressurising or even replacing.

    When the heating is on, does the pressure rise very quickly to about 3 Bar?

    I go along with the above. The expansion vessel needs repressurising.
    I used to be indecisive but now I am not sure.
  • ariba10
    ariba10 Posts: 5,432 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    Should have added that it is quite easy to do with the help of a car foot pump.
    I used to be indecisive but now I am not sure.
  • dipsy
    dipsy Posts: 3,137 Forumite
    ariba10 wrote: »
    Should have added that it is quite easy to do with the help of a car foot pump.


    Hi there, can you give me instructions :-)

    ta
    2007 £1749
    2008 £291.99
    2009 JanMasscara £7.00 Feb megcabot books x 2 £20 XFactor tkts x 2 £58.00 (couldn't go though as they only phoned on day :-( ) foundation £7.99
    total so far for 09 £92.99
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 354.4K Banking & Borrowing
  • 254.4K Reduce Debt & Boost Income
  • 455.4K Spending & Discounts
  • 247.3K Work, Benefits & Business
  • 604K Mortgages, Homes & Bills
  • 178.4K Life & Family
  • 261.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.