Another boiler question

I have had a couple of Gas Safe registered installers round to quote for the replacement of central heating boiler. I do not want a combi boiler and both installers have agred that a 15kW boiler will be sufficient for the needs of my small houe. 8 rads. eg vaillant ecoTEC plus

I was expecting to upgrade the gas pipework from 15mm to 22 mm but one installer has said that this will NOT be necessary due to the small kW size and as it will not be a combi boiler . This surprised me.

I have also been told that I will need to have either a TRV or a room stat in my lounge as currently i have neither. Stat is currently in the hallway and all other rooms have TRVs.

Can anyone confirm these findings or give me a link so I can look up the appropriate legislation for myself.
Thanks
«13

Comments

  • brig001
    brig001 Posts: 398
    Part of the Furniture 100 Posts Name Dropper Combo Breaker
    Forumite
    If you look in the Vaillant ecoTEC plus manual, you will see that the gas inlet is 15mm, so that should be fine.

    I would probably move the thermostat and fit a TRV to the hall radiator, but a second choice would be a TRV on the lounge radiator.
    A TRV can only improve the temperature control and is easy and cheap to fit while the system is drained. I don't know if it is a requirement to do it though.
    HTH,
    Brian.
  • carly
    carly Posts: 1,549
    Part of the Furniture 1,000 Posts Name Dropper
    Forumite
    thanks very much, that is reassuring. We've never bothered with a TRV in the lounge because it's too flipping cold, faces north and the room is always the coldest in the house but it wouldnt be a big job to fit one
  • latecomer
    latecomer Posts: 4,332
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Forumite
    If the room is always cold then I would check whether the radiator is of a sufficient size to heat the room.
  • carly
    carly Posts: 1,549
    Part of the Furniture 1,000 Posts Name Dropper
    Forumite
    latecomer wrote: »
    If the room is always cold then I would check whether the radiator is of a sufficient size to heat the room.

    good point. will check
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi

    The Vaillant 415 consumes gas at the rate of 1.61 m3 /h .
    It would be reasonably safe to assume that the boiler to be removed would consume a similar amount ,but your installer would check /know this.
    Your proposed installer has given you good advice.
    You should have a TRV on each rad except in the room or area where the room stat is located.

    Note to brig001.

    Just because the inlet connection is 15mm does not mean it's ok to fit 15mm pipe.
    The Ecotec 831 combi requires 3.3m3 /h of gas and has an inlet of 15mm.Run 15mm pipe to it and it will not work correctly.

    GSR.
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • heating-eng
    heating-eng Posts: 723 Forumite
    Hi

    The Vaillant 415 consumes gas at the rate of 1.61 m3 /h .
    It would be reasonably safe to assume that the boiler to be removed would consume a similar amount ,but your installer would check /know this.
    Your proposed installer has given you good advice.
    You should have a TRV on each rad except in the room or area where the room stat is located.

    Note to brig001.

    Just because the inlet connection is 15mm does not mean it's ok to fit 15mm pipe.
    The Ecotec 831 combi requires 3.3m3 /h of gas and has an inlet of 15mm.Run 15mm pipe to it and it will not work correctly.

    GSR.

    it is always best to fit trv,s but you do not have to do it and there is nothing that says you do.

    If the inlet to the boiler is 15mm then normally 15mm pipe will be ok as long as its not to far...your installer can check this to make sure..but you can normally run quite a bit of 15mm pipe on a 15kw boiler.
    you are quoting a 831 combi this is totally different.
    X British Gas engineer and X BG sales adviser.
    Please don,t let this put you off.
  • Canucklehead
    Canucklehead Posts: 6,254 Forumite
    Hi

    I thought the post was rather obviously divided into two parts.

    Perhaps you could get someone to explain it to you?


    GSR.
    Ask to see CIPHE (Chartered Institute of Plumbing & Heating Engineering)
  • gas4you
    gas4you Posts: 2,602 Forumite
    I will have to agree with canucklehead on the pipe sizing.
  • heating-eng
    heating-eng Posts: 723 Forumite
    Hi

    I thought the post was rather obviously divided into two parts.

    Perhaps you could get someone to explain it to you?


    GSR.

    can you explain where it is divided ???
    the post asks about a 15KW boiler from what i have read i might be wrong..

    but 15kw only needs 15mm gas.. i used to train BG engineers on pipe sizing for many years so i no all about pipe sizing ..Thanks
    X British Gas engineer and X BG sales adviser.
    Please don,t let this put you off.
  • ziggyman99
    ziggyman99 Posts: 431 Forumite
    can you explain where it is divided ???
    the post asks about a 15KW boiler from what i have read i might be wrong..

    but 15kw only needs 15mm gas.. i used to train BG engineers on pipe sizing for many years so i no all about pipe sizing ..Thanks
    So a 15kW boiler is OK on 40m of 15mm pipe is it? ALL installations must be correctly sized for a working pressure of 19mb or higher. A blanket statement such as yours is completely incorrect and would be frowned upon by any Gas Safe inspector.

    I'm new to gas which is why I probably do things correctly.
This discussion has been closed.
★ ★ ★ Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.8K Banking & Borrowing
  • 254.9K Reduce Debt & Boost Income
  • 456.2K Spending & Discounts
  • 248.3K Work, Benefits & Business
  • 606K Mortgages, Homes & Bills
  • 179K Life & Family
  • 263.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.