Electrical work quote

Hi,

Wonder if you could comment on whether this is a fair quote?

Materials

  • 1No. 10 W 17TH ED CONSUMER UNIT £ 65.00
  • 8No. MCB £ 20.00
  • 10No. 20MM GROMETS £ 1.00
  • 10MTR 10MM EARTH £ 10.00
  • TRUNKING £ 10.00
  • 2No. GLOBE LIGHTS £ 8.00
  • 2NO. 100W LAMPS £ 2.00
  • 2No. EARTH CLAMPS £ 2.00
  • PARKING £ 14.00

1. NO RCD PROTECTION TO CIRCUIT FED DB41B – CODE 1
ACTION INSTALL 10 WAY 17TH EDTION METALCLAD

2. MISSING EARTH BONDING TO GAS & WATER SUPPLIES – CODE 1
ACTION INSTALL 10MM EARTH CABLE FROM DB41B TO GAS AND WATER SUPPLIES

3. BATH ROOM LIGHT NOT IP RATED – CODE 1
ACTION SUPPLY & INSTALL 2No. GLOBE LIGHTS

4. NO GROMETS FITTED TO METAL BACK BOXES – CODE 2
ACTION INSTALL MISSING GROMETS

5. NO EARTH AT LIGHTING CIRCUIT TO OBTAIN TEST READINGS – CODE 3
ACTION FURTHER INVESTIGATION IN ORDER TO FIND BREAK AND ADVISE UPON FINDING ALLOWED 1 HOUR 1MAN



labour 2 peope for one day £360.00

Total including labour £578.10


This is for south london.

many thanks for the comments,

Iain

Comments

  • The lack of earth is concerning

    What make of consumer unit is it?

    The 10mm cable is a bit cheap (maybe they have old stock) as it is a bit more costly now.

    The bathroom light not being IP rated may be OK if it is above 2.27mtr (outside zone 2), or was installed to previous regs.

    Guide to domestic electrical inspection and reporting
    baldly going on...
  • fluffpot
    fluffpot Posts: 1,264 Forumite
    I wouldn't code missing grommets as a 2 - maybe 3 or 4. Besides, if your sockets are flush fitted I think it's possible to damage the cables trying to fit a grommet!
  • Hi not sure what the make the consumer unit is.

    Do you think it's a fair price? Any recommendations on where to get a second opinion?

    Is it better to give them the same details and say how much to do this or invite them round to inspect and see what they recommend to be done?

    many thanks for the responses
  • brightontraveller
    brightontraveller Posts: 1,379 Forumite
    edited 18 March 2010 at 11:52AM
    haribo1979 wrote: »
    1. NO RCD PROTECTION TO CIRCUIT FED DB41B – CODE 1
    ACTION INSTALL 10 WAY 17TH EDTION METALCLAD

    If it complied at time installation it will still be legal, but not comply with current regulation this would be a category 4 (does not comply with BS7671 2008
    (This does not imply that the electrical installation inspected is unsafe)

    I do not understand why he has this as a code 1…?

    Also is this a commercial installation ?
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.7K Banking & Borrowing
  • 253.4K Reduce Debt & Boost Income
  • 454K Spending & Discounts
  • 244.7K Work, Benefits & Business
  • 600.1K Mortgages, Homes & Bills
  • 177.3K Life & Family
  • 258.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.