boiler question

Options
I have an IDEAL classic boiler ff340 and was planning on adding a thirteenth radiator to my conservatory but I am concerned that this will be to many for the boiler. I did ring IDEAL who mentioned 40,000BTU but I don,t know how to find out how much each radiator is set at. any advice from plumbing wizards would be great.

Comments

  • derrick
    derrick Posts: 7,424 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    rooster wrote:
    I have an IDEAL classic boiler ff340 and was planning on adding a thirteenth radiator to my conservatory but I am concerned that this will be to many for the boiler. I did ring IDEAL who mentioned 40,000BTU but I don,t know how to find out how much each radiator is set at. any advice from plumbing wizards would be great.
    THIS may help, radiator sizes near bottom of page.
    Don`t steal - the Government doesn`t like the competition


  • alanobrien
    alanobrien Posts: 3,308 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker Mortgage-free Glee!
    Its also much less of an issue if you have TRV's on the rads since its probable they will not all be open / running at once.
  • derrick
    derrick Posts: 7,424 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    alanobrien wrote:
    Its also much less of an issue if you have TRV's on the rads since its probable they will not all be open / running at once.

    You would need to work on the assumption that all the valves WILL be open as at some time they will be.
    Don`t steal - the Government doesn`t like the competition


  • alanobrien
    alanobrien Posts: 3,308 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker Mortgage-free Glee!
    derrick wrote:
    You would need to work on the assumption that all the valves WILL be open as at some time they will be.


    Depends on your system. i have 14 rads and 2 of them are only on when the hot water is heating which is 1 hour a day.

    The only thing that would happen if all were running is the differential would drop, hardly something worth chnging a boiler for.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.2K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.