We’d like to remind Forumites to please avoid political debate on the Forum.
This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
Electrician - Power to Garage, Advice Please
Comments
-
Putting power to the garage is also notifiable to the council to comply with building regs as it is classed as a special location.
Personally I would ask a sparky to do the work and fit the RCD to the main incoming supply, then feed the garage supply via a new MCB, doing that you will then have full RCD protection on all circuits.You may click thanks if you found my advice useful0 -
17th Edition requires all circuits for special locations (kitchens, bathrooms, outside) to be RCD protected regardless of the RCD requiring provisions (buried 50mm in fabric of building, etc.etc.etc.) affecting circuits for other locations. So yes, it should be RCD protected at source.
RCD in the garage is protecting the garage circuits, not the supply cable!
I'm doing my 2382-10 in a months time so this has caught my interest.
Under the 17th edition regs. kitchens and 'outside' generally are not listed as special locations albeit certain outdoor installations are - basins/agricultural/marinas etc. Granted, what ever is installed at the garage would need RCD protection for the sockets, any buried cabling etc. But which reg would require the cable (presumably a distribution circuit?), if armoured, from the house to the garage to be RCD protected?
(I'm assuming it isn't a TT system and the earth fault loop impedance is low enough to ensure disconnection by the MCB within the required time)0 -
You really want us to hunt through the big red book at tea-time on a Saturday? You're the one just doing his 2382, you should be telling us!!

There's lots of debate and argument about the interpretation of a few regs which seem to contradict each other on this subject. It can be argued that if you use SWA then no RCD is needed at supply only at shed/garage but other regs then contradict this. If there is a MCB equipped CU then I'd always put it on a separate circuit, with an RCBO if no RCD.
You need to also consider whether exporting the earth is allowed to outbuildings - especially when the supply is PME! Look at 542.1.8 and 411.3.1.1 (I think, from memory) for more about exporting earths to outbuildings.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 355K Banking & Borrowing
- 254.6K Reduce Debt & Boost Income
- 455.7K Spending & Discounts
- 247.8K Work, Benefits & Business
- 604.9K Mortgages, Homes & Bills
- 178.7K Life & Family
- 262.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards