outside sockets

HELP...

i wanna install a socket on my outside wall in the garden and with all these new regulations i am not sure which cable i have to use... the cable will run along the outside wall off the house for approx 5 meters.. can i use normal pvc cable or do i have to use steel wired protected cable..??? :confused:
«1

Comments

  • Nile
    Nile Posts: 14,802 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    Hello leechip333

    Welcome to the MSE site.:wave:

    Can I ask you to read our Safety Announcement thread which is at the top of this board?

    You will be much safer if you get a qualified electrician to do this work for you. Saving money is not more important than your safety.;)

    Kind Regards

    Nile
    10 Dec 2007 - Led Zeppelin - I was there. :j [/COLOR]:cool2: I wear my 50 (gold/red/white) blood donations pin badge with pride. [/SIZE][/COLOR]Give blood, save a life. [/B]
  • leechip333
    leechip333 Posts: 8 Forumite
    lol... thanks... i am a qualified electrician just not sure of this one particular requirement.
  • economiser
    economiser Posts: 897 Forumite
    I would use pvc cable in conduit.
  • leechip333
    leechip333 Posts: 8 Forumite
    yea.. thats an idea... cheers
  • deano72_2
    deano72_2 Posts: 786 Forumite
    fp200 cable,
  • gromituk
    gromituk Posts: 3,087 Forumite
    If you're a qualified electrician, shoudn't you be consulting the IEE Regs rather than asking random people on here?:confused:
    Time is an illusion - lunch time doubly so.
  • leechip333
    leechip333 Posts: 8 Forumite
    do ya not think ive looked.... just spent the best part off 2 hours looking on the net at a number off sites....
    so gromituk if you can find any info yourself please show me where....
  • leechip333
    leechip333 Posts: 8 Forumite
    and as for fp200 cable... why on earth should i us FIRE PROOF (hence fp) for an outside installation??????
  • beefster
    beefster Posts: 742 Forumite
    Part of the Furniture 500 Posts Combo Breaker
    You will need adequate mech protection and an RCD back up at the board too.
    Did mine in SWA 2.5mm 3 core as a radial to 1x double waterproof socket with a 16A breaker.
    You could use galv or even plastic conduit with T&E cable if preffered.
    I believe an RCD at the board is a must but even if not it is a life saver.

    If you have trouble finding stuff in the regs get yourself a copy of the "on site guide to the IEE regs". Easier to follow an gives pointers to where to find additional detail in the regs.
    I save so I can spend.
  • deano72_2
    deano72_2 Posts: 786 Forumite
    leechip333 wrote:
    and as for fp200 cable... why on earth should i us FIRE PROOF (hence fp) for an outside installation??????
    its just easy to install,has the correct ip factors,dosent look as unsightly as swa.why not?
    personally i would use swa,just trying to give you another option.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.1K Banking & Borrowing
  • 253.6K Reduce Debt & Boost Income
  • 454.2K Spending & Discounts
  • 245.1K Work, Benefits & Business
  • 600.7K Mortgages, Homes & Bills
  • 177.5K Life & Family
  • 258.9K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.