ahll
Posts: 1,508 Forumite
Hi all
Getting a new kitchen fitted soon and changing from a gas cooker to a seperate electric oven and hob. The existing Consumer unit is an old one that uses BS3036 fuses (wired ones).
I am wondering if there is a good reason to updated the consumer unit ? If so can anyone recommend a good valued one that will comply with the 17th Ed for a standard sized terrace house with lights, sockets, Shower so nothing unusual.
Also what is the best way to connect an oven and hob if they both have to be hardwired ? Is there any reason you cant run cable to a Cooker Switch and then to a 63Amp juntion box then run two wires from there, one to the cooker and one to the hob ?
Getting a new kitchen fitted soon and changing from a gas cooker to a seperate electric oven and hob. The existing Consumer unit is an old one that uses BS3036 fuses (wired ones).
I am wondering if there is a good reason to updated the consumer unit ? If so can anyone recommend a good valued one that will comply with the 17th Ed for a standard sized terrace house with lights, sockets, Shower so nothing unusual.
Also what is the best way to connect an oven and hob if they both have to be hardwired ? Is there any reason you cant run cable to a Cooker Switch and then to a 63Amp juntion box then run two wires from there, one to the cooker and one to the hob ?
"The time is always right to do what is right"
0
Comments
-
Building control won't sign off a new circuit on the old fusebox, so you'll need a new one.
There are some comments on consumer unit quality and price on the "ensure your electrics" thread.0 -
I didnt realise Building Control wont sign off a new circuit on the old fusebox ! I didnt think there would be a problem as long as it was electrically safe eg right sized cable, mcb....
Has anyone had this problem ?Building control won't sign off a new circuit on the old fusebox, so you'll need a new one.
There are some comments on consumer unit quality and price on the "ensure your electrics" thread."The time is always right to do what is right"0 -
Two issues here regarding new/amended kitchen circuits and LABC (Local Authority Building Control) sign-off. Firstly the work must be done by a "competent person" (i.e. qualified/certified/registered) to BS7671:2008 17th Edition wiring regs and secondly, all new circuits in special locations (kitchens, bathrooms, outside) under the 17th edition of BS7671:2008 must be RCD protected.
No-one can force you to upgrade the old fused CU if you don't change/add any new circuits to it, but any NEW circuits must meet current regs!
However, if I were doing this job (I am an electrician) and you desperately didn't want a new CU fitting then I'd split the meter tails into a pair of Henleys, fit a new 4 way CU with RCD protection and run a dedicated radial circuit (with it's own MCB) for the kitchen sockets, another for the oven and a third for the hob. It is unwise to put hob and oven on the same radial circuit due to their potentially high individual current loading.0 -
Seems to me that there's a gap in the market for a plug-in RCBO for old Wylex boxes.
The extra connections required (to earth & neutral) would be the reason these don't exist. It wouldn't be practical (or safe) to get a DIYer (however competent) to make them, as it would entail going deep into the CU.
EDIT: Hey - where did that post I quoted go??0 -
If you decide to go for a new CU, B&Q currently have 10way Twin RCD MK 17th edition boards, fully loaded with a variety of MCBs for £80. I would be surprised if you can get a MK unit that price anywhere, could one of the electrians here confirm?
PS don't try fitting it yourself!!!!!0 -
I am not saying I wont get the CU changed I just wanted to see what my options are.
If I do what you sugesting below wouldn't I then need to have 2 separate Cooker Swtiches - One for the cooker and one for the hob ?
Previously I have not had any poblems with a cooker and hob being on the same circuit.
What do you mean when you say 'I'd split the meter tails into a pair of Henleys' ?However, if I were doing this job (I am an electrician) and you desperately didn't want a new CU fitting then I'd split the meter tails into a pair of Henleys, fit a new 4 way CU with RCD protection and run a dedicated radial circuit (with it's own MCB) for the kitchen sockets, another for the oven and a third for the hob. It is unwise to put hob and oven on the same radial circuit due to their potentially high individual current loading."The time is always right to do what is right"0 -
What do you mean when you say 'I'd split the meter tails into a pair of Henleys' ?
Sorry - electrician speak, not for DIYers! You MUST have a professional electrician to do this work - it is ALL notifiable work under Part P of the Building Regulations. With all due respect, the questions you are asking are exactly why it needs a pro. An electric hob (of any type) can easily require more than 30A on its own! Stick that on a circuit with an oven needing 15A and suddenly a 40A isolator ("cooker switch") isn't enough.0 -
I won't ralk about Part P here- different issue
It is more important to have the job done right. There may be a strong likelihood for two circuits (oven and hob) as they will probably be of a higher total rating
You should use a competent person for the work, links below
In Scotland:
Individuals registered;
http://www.sbsa.gov.uk/register/ListAC.asp
Companies
http://www.sbsa.gov.uk/register/Sear...struction&ID=2
In England and Wales:
http://www.competentperson.co.ukbaldly going on...0 -
Then a 45A can be used. If you had a free standing cooker, that has an oven and hob just there not seperate and it would have to be on the same circuit and that would be ok wouldn't it ? So whats the difference just because they are seperate ?Sorry - electrician speak, not for DIYers! You MUST have a professional electrician to do this work - it is ALL notifiable work under Part P of the Building Regulations. With all due respect, the questions you are asking are exactly why it needs a pro. An electric hob (of any type) can easily require more than 30A on its own! Stick that on a circuit with an oven needing 15A and suddenly a 40A isolator ("cooker switch") isn't enough."The time is always right to do what is right"0
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 355.3K Banking & Borrowing
- 254.7K Reduce Debt & Boost Income
- 455.9K Spending & Discounts
- 248K Work, Benefits & Business
- 605.2K Mortgages, Homes & Bills
- 178.9K Life & Family
- 263K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards