problem with ideal isar he30 boiler, help please!

Options
we have had this boiler 2.5 years with no problems, I run one of those steam room showers on it, the other night i had a steam and when i got out there was a noise coming from outside like a kettle constantly boiling checked the boiler and the pressure had dropped below 1, retopped the boiler but the noise is still there any ideas what it is and how to solve it? Thanks.

Comments

  • andyhop
    andyhop Posts: 1,996 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    The pressure drop indicates a fault or a leak

    You have topped the boiler up but the bubbling sound is the boiler kettling.You have air trapped in the heat exchanger.

    Cant remember fully about the isars as its been a while since i fitted/repaired one but it may have a release vent at the top of the boiler case near the flue. Otherwise its take the cover off and vent manually but as it means removal of the front cover and breaking the combustion seal unless your gas safe then officially you are not allowed to remove
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure
  • elmo76
    elmo76 Posts: 24 Forumite
    Would this cause water to flow out of the pipe that goes outside? as we think thats what the sound is. thanks
  • andyhop
    andyhop Posts: 1,996 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    elmo76 wrote: »
    Would this cause water to flow out of the pipe that goes outside? as we think thats what the sound is. thanks

    The safety valve will not make a kettling noise

    Get it checked out by a proffessional as the Isar is a problamatic boiler at the best of times
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure
  • elmo76
    elmo76 Posts: 24 Forumite
    Thanks a lot for the replies.:T
  • skinback69
    skinback69 Posts: 133 Forumite
    hi worked on these quite a bit and it seems to be a quite common problem with them now each time when this has happened it was the big red expansion vessle at the back of the boiler i tried re presurising them to no avail u will proberbly have to get a new one of those plus if the saftey relief valve is blowing of outside u might have to get another one of those cause they dont really reseat them selfs on these models so will always blow of even when the expansion vessel is renewed
    i think your looking at about 120 for expansion vessel may be 20 quid for blowoff valve dont know how much gas fitters will charge near you but should only take about 2 hours to fix
  • elmo76
    elmo76 Posts: 24 Forumite
    Thanks for all the replies, I'm very grateful, turns out though it wasn't the boiler at all there was a leak on the mains outside in the street, water people came and fixed it hey presto no more noises! thank goodness it wasn't the boiler! :j
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.2K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.