Baxi 105HE Combi Bolier - Re-Pressure Probs!!

Hiya, I have noticed that the pressure in my combi bolier is low. It is working ok at the moment but I have a feeling it won't be long till it falls to low for it to work. A plumber came round 6 months ago to repressurise it but did'nt show me what to do.

The plumber seems to have left the filling loop connected, but I cannot find anything to increase the pressure?? i have tried opening up the valves (there are three with "taps" on) but no luck. Am I missing something?

Has anyone got any ideas? Thanks

Comments

  • I have a Baxi 105HE. This guide describes the operation:
    Filling loop


    How to restore the pressure in a sealed heating systems

    Sealed heating systems, as are almost always found with combi boilers, need to have their pressure checked and topped up from time to time. In most cases the pressure gauge will be on the front of the boiler and should register 1.0 to 1.5 Bar.
    Over time the pressure will fall. How quickly depends on how leaky the system is. Very small leaks often occur on radiator valve spindles, Automatic Air Vents (AAVs) and other components. Often you will not notice the leak since the small amount of water will evaporate.
    Recharging the pressure once a year is probably normal, but once a month or more excessive. Every time fresh water is introduced, further scaling and corrosion may occur in the system, so you should not leave an excessively leaky system to continue.
    To recharge the system pressure you need to locate the filling loop. This is usually a silver coloured, flexible braided connection with a small valve at each end. Usually under the boiler or nearby, but sometimes incorporated into the boiler (Vaillant Turbomax Plus and some Worcesters for example).
    Having identified the filling loop, you need to work out what control valves there are. The first control valve will be nearest to the connection to the mains cold water pipe. This valve may incorporate a Double Check Valve (DCV) or be followed by it.
    Then there will be the flexible connection which is usually left connected at each end (although in theory it should be disconnected - if yours is disconnected, connect by screwing swivel nut at the end). At the other end of the flexible connection (loop) will be a DCV and/or another control valve, then the connection to the return heating pipe.
    The control valves may have plastic levers or screwdriver slots. In each case, they are on if the lever/slot is in-line with the valve (length ways) and off if the lever/slot is at right angles to the valve. There may also be a screwdriver slot on the DCV - do not unscrew this as water will be released.
    If there are 2 control valves, practice turning each one separately (no water will flow unless both are open). To recharge, open the control valve(s). You will hear the water flowing and observe the rise in pressure on the pressure gauge. Close the valve slightly if it is filling too fast. When the gauge gets to 1.0 Bar or a little over, turn the valve(s) off.
    Make sure that the valves are properly closed, preferably by disconnecting the filling loop to check that no water is flowing. Operate the boiler and check the pressure again. Any air in the boiler will vent and this may result in a drop in the pressure, requiring further topping up.
    You may also need to vent air from the radiators, particularly those at the top of the system and near the boiler. When you do this system pressure will drop again, so top up again. After this the pressure should remain fairly stable, although a slight increase on heating up of system (and drop on cooling) is normal, as is a slight change when the pump operates.





    Red
  • Thanks for your reply, i'll have a look and let you know. On your baxi combi are the 3 valves with taps all "open"?
  • There is a video here that may help-

    http://www.urlink.eu/1i
  • Yes they are open - pointing along the pipes.

    The one on the left is the output flow to the radiators
    2nd pipe (no tap) is the Hot water for the taps
    3rd pipe (no tap) is the Gas inlet
    4th pipe is the cold water in
    5th pipe is the return from the radiators.
    If you look closely there are pictograms next to each pipe.
    The filling loop is connected between the cold water in and the return from the rads


    red
  • Thanks Red & Weekend warrior for your help, managed to solve it!!:j
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.1K Banking & Borrowing
  • 252.8K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243.1K Work, Benefits & Business
  • 597.4K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 256K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.