New thermostat on radiator
rome1067
Posts: 192
Forumite
The thermostat on a bedroom radiator broke over the weekend, radiator still heats up but temperature cant be changed now.
How easy is this to replace? Do we need to drain the whole system to replace it?
Thanks
How easy is this to replace? Do we need to drain the whole system to replace it?
Thanks
0
Comments
-
The thermostat on a bedroom radiator broke over the weekend, radiator still heats up but temperature cant be changed now.
How easy is this to replace? Do we need to drain the whole system to replace it?
Thanks
.
1) pull/screw off the thermostat control (no water will come out when you do this)
2) there should be a little springed pin pointing straight up from the rad valve - this is what the thermostat moves up and down to control the water flow. Push it with your finger to check it still moves freely.
3) if it does, just put a new thermstat control on and it should work.
If the springy pin isnt moving, you need to drain the system and replace the whole valve0 -
A minor point but I would suggest using a small piece of wood or plastic or metal or a tool to very gently press it in..
1) pull/screw off the thermostat control (no water will come out when you do this)
2) there should be a little springed pin pointing straight up from the rad valve - this is what the thermostat moves up and down to control the water flow. Push it with your finger to check it still moves freely.
3) if it does, just put a new thermstat control on and it should work.
If the springy pin isnt moving, you need to drain the system and replace the whole valve
I have recently had a Myson TRV fail. It is the head that has failed. The valve itself is fine. I can easily push the little pin it with the aid of the flat of a kitchen knife but it hurts like hell if I use my finger alone.0 -
fair points from the established posters above!0
-
It shouldn't be necessary to apply percussive maintenance to the valve itself to get it to work. In any event if it was gummed up they usually fail in the closed position rather than opening up which yours appears to have done. Molegrips will wreck the pin - not recommended and its usually the spring that gets gummed up so rotating the pin won't do much for you. For those with sensitive fingers (:D) the spring is quite stiff under normal circumstances so pressure on the top using the tool suggested will work.
In what way has it "broken"? I suspect it just needs a new head.
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0
This discussion has been closed.
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards