Radiators Rapidly Filling with Sludge
AlwaysSomething
Posts: 240
Forumite
My boiler (Worcester Greenstar) and radiators are 6 years old, and had Sentinel added when new. Everything has been great until recently. Three years ago, one radiator was cold at the bottom, so I took it off and flushed it. I did this again in December. I looked at the water that came out and it was yellow in colour. Now, half of my radiators are cold at the bottom. One of them (the one without a TRV) is almost completely cold. This has happened in a matter of weeks. Can anyone suggest what might be wrong, and what to do next.
Thanks
Thanks
0
Comments
-
Have you bled them all?0
-
I don't think that's the problem, but I did open one, and there was no air in it at all.bengalknights wrote: »Have you bled them all?0 -
While the symptom you describe, of radiators that are cold at the bottom, could be attributable to sludge build up, it could equally be caused by insufficient flow through the affected radiators. Given that you say the water that came out was 'yellow' I would suggest you look for problems elsewhere as if the radiator was sludged up, the water you drained from it would have been as black as a black thing at midnight on a moonless night!
Do the remaining radiators work ok? What type of boiler is it, a combi? If not, does your hot water cylinder heat up from it ok?0 -
I have a similar problem where the rads upstairs would warm up fast and work well. However downstairs they remain cold until i turn off several radiators upstairs and very slowly will begin to heat up and the one without the TRV will be the last one to come on.
I had a plumber out since last week and he intially drained some water out from the rads downstairs and regulated the water inflow into the rads upstairs and left telling me that it should be OK. The boiler worked perfectly and he could not find anything else.
It did not solve the problem and he came round today. Tried other options and came to the conclusion that the water pump is the likely cause of the problem. The flow from the pump is not doing its job. It is a Potterton and just over 5 years old.
He will come back with a price in the next couple of days to replace the pump. I have asked him to quote a price to drain the system and radiators and fit a sludge filter at the same time as we live in a hard water area. (not power flush)
You may want to try what they did to my system before calling a qualified plumber.0 -
Thanks for your replies. It's a combi boiler, and I have plenty of hot water.
Last night I noticed that the radiator in the living room, which had been almost cold, was now quite hot. I tried an experiment. I turned off this one, and all the others except the one in the hall which was almost completely cold. I also turned the lockshield valve a quarter turn to give it a bit more flow. At the bottom left (inlet) it got hot, but only for about 1 inch. The top got just mildly warm. The bottom right (by the lockshield valve) never got warm. I opened the drain, and yellow water came out.
After turning the other rads back on, the one in the living room remains cold again, but tonight the one in the hall is quite warm on top. I seem to have a mobile blockage. Is there any way an airlock can prevent return flow from some of the rads?0 -
Option
TRV's stuck closed
Balancing issue
Incorrect rad valve installation(others still doubt this but a TRV should be fitted on the flow, yes they can be fitted so that either entry can be used which is why they are universal, but a lockshield fitted on the flow and restricted will also restrict the temperature of the radiator, LS fitted on the return means the rad will have full flow, and heat, from the TRV when required!)Signature removed0 -
Sounds very much like a flow issue. This could be down to a blockage in the pipework, a defective circulator (pump) or as has been suggested, defective TRV's or the system may just need to be balanced.
Sorry Mr T, but it doesn't make any difference if the LS valve is fitted on the flow or the return. It will still restrict the flow to the rad either way, which is its purpose anyway as it is used to balance the system.0 -
Sorry Mr T, but it doesn't make any difference if the LS valve is fitted on the flow or the return. It will still restrict the flow to the rad either way, which is its purpose anyway as it is used to balance the system.
Dont be sorry, just be right!
That is the arguement that so so many MODERN installers use who are influenced by MODERN theories by manufacturers who use UNIVERSAL as a selling point for their goods?
The fact is that if you fit a LS to the rad flow you may well ballance the system flow, BUT, all you do is restrict also the heat to the radiator which will take longer to heat, hasten the heat returning to the boiler which will shut the boiler off prematurely and all of the rad will not be up to temperature!
When you use the LS on the return the rad is getting hotter before the system and boiler stat is satified?
When the LS is on the flow and all rads are restricted on the flow the water from the boiler is going straight back to the boiler quicker and the rads wont be hot enough?
If the LS's on the flow are not restricted on upstairs rads there is every chance that downstairs rad will be bypassed especially in modern systems where drops to every downstair radiator are common?
Believe me I have been to SO MANY installations where the LS's are on the rad flow and the system has heat up and balancing problems, and EVERY ONE has been 100% OK ONCE THE RADS HAVE LS's ON THE RAD RETURNS, that is not theory that is FACT!
In most cases where this happens it is just a case of speed to install, lack of care, and a lack of knowledge and correct training!
To again exempify the scenario, if you were to do this on a commercial installation you would have BIG PROBLEMS, but on install you would also have INSTALLATION PLANS and I GUARANTEE the plan will NOT show rads with LS's on the Rad flows!!!!!!!!!!!!!!!!!!
To further exemplify, if you had to balance multiple system circuits, would you fit LS's on the flows, I DONT THINK SO, for the very same reason LS's dont belong ON FLOWS on any system!!!
Also, although being a Dinosaur not many will know, if you did this on a single pipe system, and there are still many about in commercial applications, where double regulating LS's are required (not that many of you here would have the pleasure of the knowledge of how to use them), were you to fit them on the Rad flows you would not have hot rads at all, probably, but the circuit would be lovely and hot as its where all the heat would have been diverted!!!
EXPERIENCE and GOOD QUALIFICATIONS very often blow the modern thinking out of the water, you'll learn but probably the hard way, particularly for your customers!
If you dont believe what I say, try it for yourself the next time you have a customer with heat/balancing problems and LS's on returns!Signature removed0 -
Mr T, thanks for taking the time to type all that, I appreciate the effort. While I bow to your obvious experience and knowledge, especially concerning single pipe systems (my experience with them is very limited), I'm still sorry and I'm still confident that on a typical two-pipe pumped system it makes no difference which side the LS valve goes on.
However, I firmly believe that every day is a day at school and a day that goes by when I don't learn something is a day wasted! So, please be good enough to explain why a radiator rated at approx 2kW output will behave any differently with a LS valve restricted to a mass flow of approx 0.045 litres/sec fitted on the flow side than it would if the same LS valve with the same mass flow was fitted on the return?
Just to further exemplify (to use your word! I had to look it up!!) The radiator will still have the same mass flow through it, regardless of the position of the LS valve, so it stands to reason that with the same flow the radiator will behave in exactly the same way for either scenario. Thanks in advance.0 -
When I saw the title of this thread I thought "'ere we go my problem solved" my living room radiator sounds just like the O.Ps but then when I read the replies by the 2 professionals above I lost the plot so Ill ring a plumber instead.Life is like a bath, the longer you are in it the more wrinkly you become.0
This discussion has been closed.
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards