Ready, steady… save!
You don’t need a chart to join in. Here are 2 ways to record your savings:
1. Cross it off
Pop a chart into your first post. Saved an amount? Cross it out! Read more »
£0.01 £0.02 £0.03
2. Write it down
Skip the chart and add updates to your first post. Read more »
“Another +£3 saved today. Go me!”
Use +£ before each new saving so it counts towards your total.
We’d like to remind Forumites to please avoid political debate on the Forum.
This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.
Faulty Boiler
Heath_Robinson
Posts: 95 Forumite
Really need some advice I'll try and keep the problem as short as possible:
Last night I disconnected a radiator (having a room skimmed).
Tonight I've noticed pilot light not lit
Lit pilot, start hot water or heating, everything runs for a minute (very noisily) then the pilot goes out. Tried this a couple of times and on the last time hot steamy air was coming out of some sort of release valve on the top of the boiler (it's an old worcester combi) , this continued for a while after I'd switched it off.
I assume there's a load of air in the system or something? But I wouldn't have thought this would effect hot water?
Should I reconnect the radiator and bleed the system? Since it's turned off at both ends I wouldn't have thought it should matter?
Don't really want to have to call out a heating engineer if it's something really simple...
Any help very gratefully received
Thanks
Last night I disconnected a radiator (having a room skimmed).
Tonight I've noticed pilot light not lit
Lit pilot, start hot water or heating, everything runs for a minute (very noisily) then the pilot goes out. Tried this a couple of times and on the last time hot steamy air was coming out of some sort of release valve on the top of the boiler (it's an old worcester combi) , this continued for a while after I'd switched it off.
I assume there's a load of air in the system or something? But I wouldn't have thought this would effect hot water?
Should I reconnect the radiator and bleed the system? Since it's turned off at both ends I wouldn't have thought it should matter?
Don't really want to have to call out a heating engineer if it's something really simple...
Any help very gratefully received
Thanks
0
Comments
-
No one?
The return pipe from the disconnected rad sounds empty, don't think that's right?0 -
Don't really want to have to call out a heating engineer if it's something really simple...
This IS really simple, I suspect.
Your boiler has to be full of water for the the hot water function to work and from what you've said, I suspect it isn't. The banging noise is the remaining water in the boiler actually boiling (because there's not enough water for the pump to circulate it), and the safety thermostat is doing it's job correctly and shutting off the gas including the pilot light.
The answer is simple. Replace the rad (or close both the rad valves) and refill the system. There will be a 'filling loop' somewhere. It's a short, silver-coloured flexible pipe with a valve on each end. Turn the valves on and you'll hear water rushing into the system. Watch the pressure gauge on the front of the boiler and turn the filling loop off again when the pressure has risen to 1.5 bar. Bleed the rads, top up the pressure again to 1.5 bar and your hot water function should work again.
Hope that helps, Mike0 -
You're a star! I'll try it when I get home. No one ever teaches you this stuff when you buy a house and the boiler manual wasn't helpful. My usual source of info (my dad) is working in algeria at the moment.0
This discussion has been closed.
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards