Growatt SPH6000 + 5kWh battery on Octopus Flux - why is battery discharging at 14:00 instead of waiting for my Grid First schedule (16:00-19:00)?

Setup:

  • Active mode: Load First
  • Grid First Time Period 1: 16:00-19:00 (enabled)
  • AC Charge: 02:00-05:00 (working fine - see orange bars in graph)

Problem: Blue bars show heavy discharge starting 14:00, then battery empty by peak hours when I actually need it (cooking dinner 17:00). Having to import expensive peak rate power (brown bars 17:00-19:00).

Question: How do I stop battery discharging before 16:00? Should I switch from Load First to Battery First mode? Is there a "preserve battery until X time" setting I'm missing


Comments

  • QrizB
    QrizB Posts: 20,949 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    I don't know the ins and outs of Growatt's hybrid software.
    With my Sofar, I've set it to grid charge overnight then to service loads from the battery for the rest of the day. I never force a discharge.
    But then I'm on IOG not OF.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill Coop member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • I don't use my Growatt for that sort of discharge pattern, but the image looks like a screenshot from ShinePhone. the website at https://server.growatt.com/ is a bit more user friendly and may help you achieve what you want to do better/ easier. 
  • UPDATE - SOLUTION FOUND

    Thanks for the responses. After digging through Growatt documentation and forums, I found the issue.

    The Problem: Load First mode (the system default) was discharging the battery whenever household demand exceeded solar generation - regardless of time. By the time the Grid First schedule (16:00-19:00) activated to use battery for peak period, it was already depleted.

    The Solution: Changed Load First "Discharge Stopped SOC" from 10% to 90%

    This tells the system: "Don't discharge battery during the day unless it drops below 90%"

    The Grid First schedule (16:00-19:00) overrides this restriction, so battery still discharges during peak hours as intended.

    In practice:

    • Battery charges overnight to 100% (02:00-05:00) ✅
    • During day, Load First sees battery >90% and WON'T discharge it (preserves charge)
    • House uses solar or standard-rate grid during day
    • At 16:00 Grid First forces discharge regardless of SOC
    • Battery available for expensive peak period (16:00-19:00) ✅

    Will report back in a few days to confirm if this resolves the early discharge issue.

Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 353.1K Banking & Borrowing
  • 254K Reduce Debt & Boost Income
  • 454.8K Spending & Discounts
  • 246.2K Work, Benefits & Business
  • 602.3K Mortgages, Homes & Bills
  • 177.8K Life & Family
  • 260.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.