In my opinion if you mention a phase to earth fault tripping the mcb and the rcd has not tripped then the electrician could think you just do not know what you are talking about!Whilst it is theoretically not impossible, it is most unlikely that a phase to earth fault will trip the mcb and not the rcd. The mcb is there to protect the wiring should a fault occur I.e. in your case a sustained current being passed significantly more than 16Amps. This is to prevent the build up of heat in the wiring, damaging the cable or (as above mentioned ) causing a fire. It should not be bypassed or attempts made to override it.The rcd is specifically there to detect a fault current between either or both phase carrying wires ( live and neutral in your case ). It is very sensitive and will operate very quickly ( thousandths of a second) for a fault current of thousandths of an Amp.This post is just given as a guide to help explain the main differences between an rcd and mcd and the protection thus provided ( leakage/shock for rcd and overcurrent/ short circuit for mcb). Do not take it as being all there us to it as it is a bit more complicated than the above!!0
-
I will make no claims with regard to my level of technical expertise when the electrician comes. Such as the difference in function between the two devices as you have explained. Clearly the task is to identify the source of the tripping which appears to affect the mcb more often than the rcb. I just wonder if one can regard the solar pv inverter circuit as separate from the main house wiring circuit (lower voltage?)Telegraph Sam
There are also unknown unknowns - the one's we don't know we don't know0 -
For what it’s worth, I would have brought in a PV engineer rather than a general sparky. The fault may lie in the inverter4.8kWp 12x400W Longhi 9.6 kWh battery Giv-hy 5.0 Inverter, WSW facing Essex . Aint no sunshine ☀️ Octopus gas fixed dec 24 @ 5.74 tracker again+ Octopus Intelligent Flux leccy0
-
I may resort to that if the electrician can't sort it. Trouble is that PV engineers are a bit thin on the ground hereTelegraph Sam
There are also unknown unknowns - the one's we don't know we don't know0 -
.Heedtheadvice said:
Whilst waiting for my electrician to make an appearance I am increasingly coming to the view that the above comment could be at the root of it. In the sense that the MCB tends to trip with the onset of strong daylight hours, but will begin to behave itself again when the strength of the daylight wanes. In which case my investment in a replacement RCB and MCB could turn out to be wrong.Whilst it is theoretically not impossible, it is most unlikely that a phase to earth fault will trip the mcb and not the rcd. The mcb is there to protect the wiring should a fault occur I.e. in your case a sustained current being passed significantly more than 16Amps. This is to prevent the build up of heat in the wiring, damaging the cable or (as above mentioned ) causing a fire. It should not be bypassed or attempts made to override it.The rcd is specifically there to detect a fault current between either or both phase carrying wires ( live and neutral in your case ). It is very sensitive and will operate very quickly ( thousandths of a second) for a fault current of thousandths of an Amp.This post is just given as a guide to help explain the main differences between an rcd and mcd and the protection thus provided ( leakage/shock for rcd and overcurrent/ short circuit for mcb). Do not take it as being all there us to it as it is a bit more complicated than the above!!
Main thing is to get it sorted.Telegraph Sam
There are also unknown unknowns - the one's we don't know we don't know0 -
Telegraph_Sam said:Main thing is to get it sorted.When exactly is your electrician due to visit? What date have you agreed?You've had this problem for more than a month and it could easily have cost you £300 already in lost FIT payments (based on a south facing 4kWp system near Newcastle, expected to generate 100kWh a week in July and August, and a 75p FIT).N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!0 -
QrizB said:Telegraph_Sam said:Main thing is to get it sorted.When exactly is your electrician due to visit? What date have you agreed?You've had this problem for more than a month and it could easily have cost you £300 already in lost FIT payments (based on a south facing 4kWp system near Newcastle, expected to generate 100kWh a week in July and August, and a 75p FIT).Living the dream in the Austrian Alps.0
-
Looks like my electrician has done a vanishing act. I"ll need to find a replacement.
I doubt that I'm "losing'" anything like the £££'s you mention. Small consolationTelegraph Sam
There are also unknown unknowns - the one's we don't know we don't know0 -
If it is tripping out when it is sunny, I'd suggest monitoring your local voltage. If you see more than about 3 volts variance and the voltage rises to 253V or more, then it is very likely a high impedance fault in your local network. If you find that to be the case then ring your DNO, who will monitor your voltage, and make a repair, if necessary.
When I had a similar problem it was fixed in less than a week from my phone call and cost nothing.0 -
I don't think the system knows what it is doing, the performance is not constant. I will obviously have to get it checked out by an electrician (endangered species).
How easy is it to measure the voltage, and how? Or I can just ring Northern Powergrid and get them to check - which may or may not resolve the tripping problem.Telegraph Sam
There are also unknown unknowns - the one's we don't know we don't know0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.5K Banking & Borrowing
- 253.3K Reduce Debt & Boost Income
- 453.9K Spending & Discounts
- 244.5K Work, Benefits & Business
- 599.8K Mortgages, Homes & Bills
- 177.2K Life & Family
- 258.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards