Solar iboost system - being charged for 'free' hot water

Options
1235

Comments

  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    You are quite right Mr Chaser....what you suspect is a possibility  but some of the descriptions  of the 'fault' and answers to questions don't really give enough detail to be definitive. There has been, for example, only an indication that the problem exists when PV  is being generated. That would imply CT OK and main unit faulty - or something else!
    So that should be answered by Test 2 that I copied into a post.

    I wish Reggieboy  would have answered the questions 'in full' ( to quote Martin Lewis ) and be more descriptive and post pictures where that would help for us to see.

    Several of  us have been helping and suggesting along similar lines to check/test and rule things out.

    I am wondering if I am wasting time and I am  near the stage of stopping  hitting my head off the brick wall.

    Reggieboy please do what Solarchaser suggests. It might be the problem but if it is not the problem lies elsewhere.....and do bear in  mind that it sometimes takes a few seconds for readings to show up correctly.
    I guessed from your earlier replies (that i liked) that you were getting a little... frustrated with lack of answers,  that's why I figured a quick test may confirm one way or the other.

    I mean from a service engineer point of view it's pretty clear from the replies from folk who have read the manual, the device doesn't (shouldnt) do full power for any excess, it should be excess power only.

    So as has been stated a few times, either the clamp is in the wrong place, or the wrong way round... hence the unanswered picture requests, or the unit is faulty.
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    Qyburn said:
    Hi guys

    Problem still exists, been advised from Marlec (the manufacturer) to try the clamp on a different tail, but cannot fit it on specified cable as there's no room for the clamp, don't know what to do next
    Cheers again
    The CT clamp is labelled to show which way round it should go, assuming it's on the Live tail. It will work equally well on Neutral but would need to be fitted the other way round.
    This is probably true, but its more common than you would want to think, to have your live and neutral tails mislabelled / wired wrong.

    My house was the wrong way round for years without me knowing, I only found out when a different smart meter was to be fitted, and the lad pointed out my first smart meter was wired with neutral in live and vice versa 🤷‍♂️
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • Heedtheadvice
    Heedtheadvice Posts: 2,774 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    You are quite right Mr Chaser....what you suspect is a possibility  but some of the descriptions  of the 'fault' and answers to questions don't really give enough detail to be definitive. There has been, for example, only an indication that the problem exists when PV  is being generated. That would imply CT OK and main unit faulty - or something else!
    So that should be answered by Test 2 that I copied into a post.

    I wish Reggieboy  would have answered the questions 'in full' ( to quote Martin Lewis ) and be more descriptive and post pictures where that would help for us to see.

    Several of  us have been helping and suggesting along similar lines to check/test and rule things out.

    I am wondering if I am wasting time and I am  near the stage of stopping  hitting my head off the brick wall.

    Reggieboy please do what Solarchaser suggests. It might be the problem but if it is not the problem lies elsewhere.....and do bear in  mind that it sometimes takes a few seconds for readings to show up correctly.
    I guessed from your earlier replies (that i liked) that you were getting a little... frustrated .....

    Yes it's the Victor Meldrew coming out in me 😀
  • Qyburn
    Qyburn Posts: 3,638 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    I think it would misbehave even more wildly if the clamp was the wrong way round.
  • Dave_Fowler
    Dave_Fowler Posts: 626 Forumite
    Part of the Furniture 500 Posts Name Dropper
    Qyburn said:
    I think it would misbehave even more wildly if the clamp was the wrong way round.
    Absolutely correct. It would turn on whenever the house was drawing power from the grid.
    It is behaving as if the clamp is on the solar output cable - as soon as there is any solar output the iboost is turning on, and without any feedback from the grid cable it would ramp up the current sent to the immersion to maximum using the time-constant designed into the iboost. In my setup this is about 8 seconds.
    Solar PV System 1: 2.96kWp South+8 degrees. Roof 38 degrees. 'Normal' system
    Solar PV System 2: 3.00kWp South-4 degrees. Roof 28 degrees. SolarEdge system
    EV car, PodPoint charger
    Lux LXP 3600 ACS + 6 x 2.4kWh Aoboet LFP 2400 battery storage. Installed Feb 2021
    Location: Bedfordshire
  • paul991
    paul991 Posts: 451 Forumite
    Third Anniversary 100 Posts
    Best way to sort this out would to be a photo of the  cables and where the clamp is situated. Is it on the right cable . ie not on a dual supply cable
  • Qyburn
    Qyburn Posts: 3,638 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    Qyburn said:
    I think it would misbehave even more wildly if the clamp was the wrong way round.
    Absolutely correct. It would turn on whenever the house was drawing power from the grid.
    It is behaving as if the clamp is on the solar output cable - as soon as there is any solar output the iboost is turning on, and without any feedback from the grid cable it would ramp up the current sent to the immersion to maximum using the time-constant designed into the iboost. In my setup this is about 8 seconds.
    Right, so the clamp could be on the inverter output, not the meter tail.
  • Reggieboy2025
    Reggieboy2025 Posts: 15 Forumite
    10 Posts
    Hi guys,
     Quick update, so electrician called round today , he moved the clamp onto the mains cable where all the electricity enters /exits the property,he also turned the clamp the other way round (meter arrow pointing away from the meter) and hallelujah it's finally working as intended.

    Many thanks for all you guys help
    Much appreciated 
  • Reed_Richards
    Reed_Richards Posts: 5,355 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    How do we explain this?
    Reed
  • QrizB
    QrizB Posts: 18,442 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    How do we explain this?
    Clamp was on the wrong bit of tails. Whichever bit it was on, it was measuring solar generation but not measuring the load applied by the water heater.
    A photo would make everything clearer (and might have let us spot the problem on page 1 of the thread).
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.2K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.3K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.